  2. L+G E355 Load Control
By DuddyS , 28 August, 2026
We have an L+G E355 meter with a main (primary) contactor controllable via "0.0.96.3.10.255" object/attributes that works perfectly using gxDlmsDisconnectControl.(RemoteDisconnect and RemoteReconnect).
However, the meter has also has a load control (secondary low load) relay that we are still unable to control.
Do you have any suggestion around this main contactor/load relay scenario as all the topics I have viewed seem to be related to the primary contactor and that is not our issue.
It may simply be I a, not using the correct OBIS code for this operation, but discovery of this information is very elusive.
16 sec ago
Hi, You use load control in…
You use load control in the same way as you use "0.0.96.3.10.255". You just need to change the OBIS code to the correct one.
Read your meter with GXDLMSDirector, and you can see the correct OBIS code and also that RemoteDisconnect and RemoteReconnect are available.
  • L+G E355 Load Control
  • Generic Exception raised on HLS authentication failure instead of GXDLMSException
  • DLMS Image Transfer: “byte must be in range(0, 256)” with 512-byte block size in Python
  • Connecting to meter using Wrapper
  • DLMS Server / Meter emulation in Golang library