  2. Association LN Attributes List
Association LN attributes list
By jan.kolar , 20 September, 2023
i am writing software for configuration of meters which will be used for various meter types from different manufacturers. One of the key operations of this software will be to read association view from the connected meter. Based on it will display parameter tree with all supported OBIS codes, attributes and methods. I face problem with meter Landis&Gyr E550. It returns list of all objects but the list of attributes and methods is always empty. This happens when using Gurux DLMS Director and also when using our own software which is based on C++ Gurux library. What is your experience with different meter types ? Is this behavior manufacturer-specific or I used incorrect request ?
All the items in association view looks similar to this (notice empty arrays):
DLMS_PDU[196] {** GetResponse **}
└──GetResponse[1] {** Get-response-normal **}
└──GetResponseNormal Sequence
├──InvokeIdPriority
│ ├──InvokeID (0..3): 1
│ ├──ServiceClass (6): confirmed
│ └──Priority (7): high
└──GetDataResult Result[0] {** data **}
└──Data[1] {** Array **}
└──SequenceOf 271 Element(s)
├──0: Data[2] {** Structure **}
│ └──SequenceOf 4 Element(s)
│ ├──0: [18] Unsigned16 = 10009 (0x2719)
│ ├──1: [17] Unsigned8 = 82 (0x52)
│ ├──2: [9] OctetString[6] = 00 00 F0 3A FF FF
│ └──3: Data[2] {** Structure **}
│ └──SequenceOf 2 Element(s)
│ ├──0: Data[1] {** Array **}
│ │ └──SequenceOf 0 Element(s)
│ └──1: Data[1] {** Array **}
├──1: Data[2] {** Structure **}
│ ├──0: [18] Unsigned16 = 3 (0x0003)
│ ├──1: [17] Unsigned8 = 0 (0x00)
│ ├──2: [9] OctetString[6] = 00 00 61 61 00 FF
What I don't understand is how Gurux DLMS Director determine list of attributes and their access rights (see attached screenshot) ? How can I populate list of attributes and methods in my software ? Of course there is option to populate it based on class_id which is defined in standard but this method cannot be used with manufacturer-specific objects. Also this approach cannot reliably determine if some attribute supports read-write access or only read access (without actually trying to change its value).
Attaching logs from Gurux DLMS Director:
GXDLMSDirector 9.0.2308.1601
Log created 6:19:47 AM
06:21:36 Initializing serial connection.
06:21:37 IEC Sending:/?!<CR><LF>
06:21:39 HDLC received: /LGZ5\2ZMG310041b.P07<CR><LF>
06:21:39 BaudRate is : 9600
6:21:39 AM Moving to mode E.
06 32 35 32 0D 0A
6:21:42 AM Send SNRM request.
7E A0 07 03 A1 93 C3 8D 7E
6:21:42 AM
7E A0 1E A1 03 73 2F 76 81 80 12 05 01 80 06 01 3E 07 04 00 00 00 01 08 04 00 00 00 01 07 22 7E
06:21:42 Parsing UA reply succeeded.
6:21:42 AM Send AARQ request.
7E A0 2B 03 A1 10 37 23 E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 62 1C 5D FF FF FE 6C 7E
6:21:42 AM
7E A0 37 A1 03 30 80 70 E6 E7 00 61 28 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 0F 04 0D 08 00 06 5F 1F 04 00 00 00 18 13 88 00 07 6E 27 7E
06:21:42 Parsing AARE reply succeeded.
6:21:46 AM Read object type AssociationLogicalName index: 2
7E A0 19 03 A1 32 A3 54 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 02 00 91 53 7E
6:21:46 AM
7E A8 53 A1 03 52 BC 81 E6 E7 00 C4 01 C1 00 01 82 01 0F 02 04 12 27 19 11 52 09 06 00 00 F0 3A FF FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 61 61 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 F0 0C FF 02 02 01 00 01 00 F6 09 7E
06:21:46 Get next frame.
7E A0 07 03 A1 51 DD 68 7E
6:21:46 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 07 11 01 09 06 01 00 63 62 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 01 00 63 01 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 01 00 63 02 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 7E 02 02 01 00 01 00 3C B7 7E
7E A0 07 03 A1 71 DF 49 7E
6:21:47 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 08 11 00 09 06 00 00 01 00 00 FF 02 02 01 00 01 00 02 04 12 2A 94 11 00 09 06 01 01 63 62 96 FF 02 02 01 00 01 00 02 04 12 2A 9E 11 00 09 06 01 01 63 62 81 FF 02 02 01 00 01 00 02 04 12 2A 9E 11 00 09 06 01 01 63 62 82 FF 02 02 01 00 01 00 0E 3A 7E
06:21:47 Get next frame.
6:21:47 AM Read object type AssociationLogicalName index: 2
7E A0 07 03 A1 91 D1 AE 7E
6:21:47 AM
7E A8 5D A1 03 58 A4 80 02 04 12 2A 9E 11 00 09 06 01 01 63 62 83 FF 02 02 01 00 01 00 02 04 12 2A 9E 11 00 09 06 01 01 63 62 88 FF 02 02 01 00 01 00 02 04 12 2A 9E 11 00 09 06 01 01 63 62 8D FF 02 02 01 00 01 00 02 04 12 2A A8 11 00 09 06 01 01 63 62 89 FF 02 02 01 00 01 00 99 36 7E
7E A0 07 03 A1 B1 D3 8F 7E
6:21:47 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 2A A8 11 00 09 06 01 01 63 62 8A FF 02 02 01 00 01 00 02 04 12 2A BC 11 00 09 06 01 01 63 62 95 FF 02 02 01 00 01 00 02 04 12 2A C6 11 00 09 06 01 01 63 62 94 FF 02 02 01 00 01 00 02 04 12 2A D0 11 01 09 06 01 01 63 62 97 FF 02 02 01 00 01 00 0A BC 7E
7E A0 07 03 A1 D1 D5 EC 7E
6:21:47 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 2A BD 11 00 09 06 01 01 63 62 A1 FF 02 02 01 00 01 00 02 04 12 2A BD 11 00 09 06 01 01 63 62 A2 FF 02 02 01 00 01 00 02 04 12 2A BD 11 00 09 06 01 01 63 62 A3 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 00 00 FF 02 02 01 00 01 00 51 E5 7E
7E A0 07 03 A1 F1 D7 CD 7E
6:21:47 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 01 11 00 09 06 01 00 00 00 01 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 00 02 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 00 03 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 00 FF 02 02 01 00 01 00 35 2D 7E
7E A0 07 03 A1 11 D9 2A 7E
6:21:47 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 01 11 00 09 06 00 00 60 01 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 02 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 01 60 02 05 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 02 02 FF 02 02 01 00 01 00 89 5C 7E
7E A0 07 03 A1 31 DB 0B 7E
6:21:47 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 01 11 00 09 06 00 00 60 F0 00 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 00 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 01 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 5A FF FF 02 02 01 00 01 00 75 C0 7E
6:21:48 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 01 11 00 09 06 00 00 2A 00 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 01 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 01 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 01 08 03 FF 02 02 01 00 01 00 33 B2 7E
06:21:48 Get next frame.
6:21:48 AM Read object type AssociationLogicalName index: 2
6:21:48 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 03 11 00 09 06 01 01 05 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 05 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 05 08 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 06 08 01 FF 02 02 01 00 01 00 75 1B 7E
6:21:48 AM
7E A8 5D A1 03 58 A4 80 02 04 12 00 03 11 00 09 06 01 01 06 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 06 08 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 07 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 07 08 02 FF 02 02 01 00 01 00 41 75 7E
6:21:48 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 03 11 00 09 06 01 01 07 08 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 08 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 08 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 08 08 03 FF 02 02 01 00 01 00 5B A4 7E
6:21:48 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 03 11 00 09 06 01 01 02 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 02 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 02 08 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 1F 08 01 FF 02 02 01 00 01 00 73 9F 7E
6:21:48 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 03 11 00 09 06 01 01 33 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 47 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 01 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 02 08 00 FF 02 02 01 00 01 00 6D 43 7E
6:21:48 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 03 11 00 09 06 01 01 05 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 06 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 07 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 08 08 00 FF 02 02 01 00 01 00 1F 38 7E
6:21:49 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 03 11 00 09 06 01 01 03 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 04 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 15 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 29 08 00 FF 02 02 01 00 01 00 E9 B8 7E
06:21:49 Get next frame.
6:21:49 AM Read object type AssociationLogicalName index: 2
6:21:49 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 03 11 00 09 06 01 01 3D 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 1F 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 33 08 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 47 08 00 FF 02 02 01 00 01 00 10 B0 7E
6:21:49 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 03 11 00 09 06 00 00 60 08 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 08 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 08 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 08 00 FF 02 02 01 00 01 00 8E 3C 7E
6:21:49 AM
7E A8 5D A1 03 58 A4 80 02 04 12 00 03 11 00 09 06 00 00 60 02 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 F0 1E 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 00 01 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 01 FF 02 02 01 00 01 00 59 88 7E
6:21:49 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 03 11 00 09 06 00 00 60 07 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 F0 1E 02 FF 02 02 01 00 01 00 1B 2F 7E
6:21:49 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 03 11 00 09 06 00 00 F0 1E 03 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 06 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 01 60 06 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 F0 1E 11 FF 02 02 01 00 01 00 2D F1 7E
6:21:50 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 05 11 00 09 06 01 01 01 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 02 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 05 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 06 04 00 FF 02 02 01 00 01 00 69 96 7E
06:21:50 Get next frame.
6:21:50 AM Read object type AssociationLogicalName index: 2
6:21:50 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 05 11 00 09 06 01 01 07 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 08 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 03 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 01 04 04 00 FF 02 02 01 00 01 00 0F 16 7E
6:21:50 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 04 11 00 09 06 01 01 01 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 01 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 01 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 02 06 01 FF 02 02 01 00 01 00 00 2C 7E
6:21:50 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 04 11 00 09 06 01 01 02 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 02 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 05 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 05 06 02 FF 02 02 01 00 01 00 7C 24 7E
6:21:50 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 04 11 00 09 06 01 01 05 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 08 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 08 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 08 06 03 FF 02 02 01 00 01 00 9D 96 7E
6:21:50 AM
7E A8 5D A1 03 58 A4 80 02 04 12 00 04 11 00 09 06 01 01 01 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 03 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 04 06 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 20 07 00 FF 02 02 01 00 01 00 3E A9 7E
6:21:50 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 03 11 00 09 06 01 01 34 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 48 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 5B 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 1F 07 00 FF 02 02 01 00 01 00 D6 1E 7E
6:21:51 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 03 11 00 09 06 01 01 33 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 47 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 0E 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 51 07 00 FF 02 02 01 00 01 00 EA 45 7E
06:21:51 Get next frame.
6:21:51 AM Read object type AssociationLogicalName index: 2
6:21:51 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 03 11 00 09 06 01 01 51 07 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 51 07 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 51 07 04 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 51 07 05 FF 02 02 01 00 01 00 B9 6A 7E
6:21:51 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 03 11 00 09 06 01 01 51 07 06 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 10 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 24 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 38 07 00 FF 02 02 01 00 01 00 12 B9 7E
6:21:51 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 03 11 00 09 06 01 01 4C 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 83 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 97 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 AB 07 00 FF 02 02 01 00 01 00 DA AD 7E
6:21:51 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 03 11 00 09 06 01 01 BF 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 09 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 1D 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 31 07 00 FF 02 02 01 00 01 00 7F BA 7E
6:21:51 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 03 11 00 09 06 01 01 45 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 0D 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 21 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 35 07 00 FF 02 02 01 00 01 00 87 8E 7E
6:21:51 AM
7E A8 5D A1 03 58 A4 80 02 04 12 00 03 11 00 09 06 01 01 49 07 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 0B FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 0C FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 07 0D FF 02 02 01 00 01 00 1B 1F 7E
6:21:52 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 03 11 00 09 06 00 00 60 07 0A FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 20 1A 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 34 1A 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 48 1A 00 FF 02 02 01 00 01 00 15 F6 7E
06:21:52 Get next frame.
6:21:52 AM Read object type AssociationLogicalName index: 2
6:21:52 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 04 11 00 09 06 01 01 20 17 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 34 17 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 48 17 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 1F 1A 00 FF 02 02 01 00 01 00 09 03 7E
6:21:52 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 04 11 00 09 06 01 01 33 1A 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 47 1A 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 20 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 34 06 00 FF 02 02 01 00 01 00 BB 96 7E
6:21:52 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 04 11 00 09 06 01 01 48 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 20 03 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 34 03 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 01 48 03 00 FF 02 02 01 00 01 00 62 BF 7E
6:21:52 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 04 11 00 09 06 01 01 01 80 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 20 23 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 34 23 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 48 23 00 FF 02 02 01 00 01 00 0B 0F 7E
6:21:52 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 00 15 11 00 09 06 01 01 20 1F 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 34 1F 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 48 1F 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 5B 23 00 FF 02 02 01 00 01 00 1D 5E 7E
6:21:53 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 15 11 00 09 06 01 01 1F 23 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 33 23 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 47 23 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 20 1F 02 FF 02 02 01 00 01 00 B3 CA 7E
06:21:53 Get next frame.
6:21:53 AM Read object type AssociationLogicalName index: 2
6:21:53 AM
7E A8 5D A1 03 58 A4 80 02 04 12 00 15 11 00 09 06 01 01 20 1F 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 20 23 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 20 23 02 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 34 1F 02 FF 02 02 01 00 01 00 4F DA 7E
6:21:53 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 15 11 00 09 06 01 01 34 1F 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 34 23 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 34 23 02 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 48 1F 02 FF 02 02 01 00 01 00 28 8F 7E
6:21:53 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 15 11 00 09 06 01 01 48 1F 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 48 23 01 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 01 01 48 23 02 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 00 03 00 FF 02 02 01 00 01 00 E9 CF 7E
6:21:53 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 03 11 00 09 06 01 01 00 03 01 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 01 00 06 00 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 F0 1E 09 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 F0 1E 0A FF 02 02 01 00 01 00 CF 26 7E
6:21:53 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 01 11 00 09 06 00 00 F0 1E 12 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 F0 1E 0B FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 F0 1E 0C FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 F0 1E 13 FF 02 02 01 00 01 00 C0 5F 7E
6:21:53 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 00 01 11 00 09 06 00 00 60 63 08 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 04 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 5A 01 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 01 02 FF 02 02 01 00 01 00 9E BC 7E
6:21:54 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 27 48 11 00 09 06 00 00 F0 06 00 FF 02 02 01 00 01 00 02 04 12 27 48 11 00 09 06 00 01 F0 06 00 FF 02 02 01 00 01 00 02 04 12 27 48 11 00 09 06 00 00 F0 06 07 FF 02 02 01 00 01 00 02 04 12 27 48 11 00 09 06 00 00 F0 06 08 FF 02 02 01 00 01 00 69 68 7E
06:21:54 Get next frame.
6:21:54 AM Read object type AssociationLogicalName index: 2
6:21:54 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 03 11 00 09 06 00 00 60 04 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 05 00 FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 01 FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 02 FF 02 02 01 00 01 00 9F E9 7E
6:21:54 AM
7E A8 5D A1 03 58 A4 80 02 04 12 29 86 11 51 09 06 00 00 F0 05 03 FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 04 FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 07 FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 08 FF 02 02 01 00 01 00 76 36 7E
6:21:54 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 29 86 11 51 09 06 00 00 F0 05 0B FF 02 02 01 00 01 00 02 04 12 29 86 11 51 09 06 00 00 F0 05 0C FF 02 02 01 00 01 00 02 04 12 27 2A 11 50 09 06 01 02 52 08 00 FF 02 02 01 00 01 00 02 04 12 27 2A 11 50 09 06 01 03 52 08 00 FF 02 02 01 00 01 00 6D B3 7E
6:21:54 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 27 29 11 50 09 06 00 01 60 03 04 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 00 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 10 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 20 FF 02 02 01 00 01 00 DB E1 7E
6:21:54 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 21 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 22 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 23 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 24 FF 02 02 01 00 01 00 B9 D7 7E
6:21:54 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 27 FF 02 02 01 00 01 00 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 30 FF 02 02 01 00 01 00 02 04 12 27 1B 11 01 09 06 00 00 F0 0E 31 FF 02 02 01 00 01 00 02 04 12 27 43 11 00 09 06 00 00 F0 0E 32 FF 02 02 01 00 01 00 5E FB 7E
6:21:55 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 27 1A 11 01 09 06 00 00 F0 0E 36 FF 02 02 01 00 01 00 02 04 12 27 1B 11 01 09 06 00 00 F0 0E 37 FF 02 02 01 00 01 00 02 04 12 27 20 11 01 09 06 00 00 F0 0E 60 FF 02 02 01 00 01 00 02 04 12 27 B6 11 50 09 06 00 00 F0 09 FF FF 02 02 01 00 01 00 E1 00 7E
06:21:55 Get next frame.
6:21:55 AM Read object type AssociationLogicalName index: 2
6:21:55 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 27 26 11 50 09 06 00 00 F0 08 00 FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 01 FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 02 FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 03 FF 02 02 01 00 01 00 4C 2F 7E
6:21:55 AM
7E A8 5D A1 03 56 DA 69 02 04 12 27 26 11 50 09 06 00 00 F0 08 04 FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 0A FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 0E FF 02 02 01 00 01 00 02 04 12 27 26 11 50 09 06 00 00 F0 08 0F FF 02 02 01 00 01 00 04 25 7E
6:21:55 AM
7E A8 5D A1 03 58 A4 80 02 04 12 27 12 11 52 09 06 00 00 F0 00 FF FF 02 02 01 00 01 00 02 04 12 27 60 11 04 09 06 00 00 F0 0F FF FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 09 05 FF 02 02 01 00 01 00 02 04 12 27 6F 11 00 09 06 00 00 00 00 00 00 02 02 01 00 01 00 B2 C3 7E
6:21:55 AM
7E A8 5D A1 03 5A B6 A3 02 04 12 00 14 11 00 09 06 00 00 0D 00 00 FF 02 02 01 00 01 00 02 04 12 00 0B 11 00 09 06 00 00 0B 00 00 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 00 02 07 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 02 07 FF 02 02 01 00 01 00 0C 8B 7E
6:21:55 AM
7E A8 5D A1 03 5C 80 C6 02 04 12 00 1B 11 00 09 06 00 00 02 00 00 FF 02 02 01 00 01 00 02 04 12 00 1C 11 00 09 06 00 00 02 02 00 FF 02 02 01 00 01 00 02 04 12 4E 54 11 50 09 06 00 00 F0 14 FF FF 02 02 01 00 01 00 02 04 12 27 95 11 50 09 06 00 00 F0 3B FF FF 02 02 01 00 01 00 0A 42 7E
6:21:56 AM
7E A8 5D A1 03 5E 92 E5 02 04 12 00 01 11 00 09 06 00 00 F0 13 01 FF 02 02 01 00 01 00 02 04 12 00 17 11 00 09 06 00 00 16 00 00 FF 02 02 01 00 01 00 02 04 12 00 17 11 00 09 06 00 01 16 00 00 FF 02 02 01 00 01 00 02 04 12 00 17 11 00 09 06 00 02 16 00 00 FF 02 02 01 00 01 00 AE 9E 7E
06:21:56 Get next frame.
6:21:56 AM Read object type AssociationLogicalName index: 2
6:21:56 AM
7E A8 5D A1 03 50 EC 0C 02 04 12 00 13 11 00 09 06 00 00 14 00 00 FF 02 02 01 00 01 00 02 04 12 00 13 11 00 09 06 00 00 14 00 01 FF 02 02 01 00 01 00 02 04 12 00 13 11 00 09 06 00 02 14 00 01 FF 02 02 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 08 FF 02 02 01 00 01 00 62 2C 7E
6:21:56 AM
7E A8 5D A1 03 52 FE 2F 02 04 12 27 33 11 00 09 06 00 00 60 06 04 FF 02 02 01 00 01 00 02 04 12 27 1E 11 50 09 06 00 01 60 06 03 FF 02 02 01 00 01 00 02 04 12 00 0C 11 00 09 06 00 00 28 00 01 FF 02 02 01 00 01 00 02 04 12 00 0F 11 00 09 06 00 00 28 00 00 FF 02 02 01 00 01 00 54 DD 7E
6:21:56 AM
7E A8 5D A1 03 54 C8 4A 02 04 12 27 21 11 52 09 06 00 00 F0 0A FF FF 02 02 01 00 01 00 02 04 12 27 24 11 51 09 06 00 00 F0 0C FF FF 02 02 01 00 01 00 02 04 12 27 22 11 50 09 06 00 00 F0 03 FF FF 02 02 01 00 01 00 02 04 12 27 74 11 52 09 06 00 00 F0 01 FF FF 02 02 01 00 01 00 17 B1 7E
6:21:56 AM
7E A8 5D A1 03 56 DA 69 02 04 12 00 11 11 00 09 06 00 00 29 00 00 FF 02 02 01 00 01 00 02 04 12 27 38 11 51 09 06 00 00 F0 07 FF FF 02 02 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 00 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 65 FF 02 02 01 00 01 00 C2 8D 7E
6:21:56 AM
7E A0 5D A1 03 58 84 DA 02 04 12 00 09 11 00 09 06 00 00 0A 00 66 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 68 FF 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 5A 02 FF 02 02 01 00 01 00 02 04 12 29 72 11 01 09 06 00 00 F0 21 FF FF 02 02 01 00 01 00 88 F0 7E
6:21:56 AM Read object type AssociationLogicalName index: 3
7E A0 19 03 A1 B4 9D B5 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 03 00 49 4A 7E
6:21:57 AM
7E A0 17 A1 03 7A 8D 12 E6 E7 00 C4 01 C1 00 02 02 0F 50 12 00 01 5C 2A 7E
6:21:57 AM Read object type AssociationLogicalName index: 4
7E A0 19 03 A1 D6 89 F5 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 04 00 41 07 7E
6:21:57 AM
7E A0 21 A1 03 9C DD 97 E6 E7 00 C4 01 C1 00 02 07 11 02 11 10 12 02 F4 11 05 11 08 11 01 11 01 3A 58 7E
6:21:57 AM Read object type AssociationLogicalName index: 5
7E A0 19 03 A1 F8 F5 3D E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 05 00 99 1E 7E
6:21:57 AM
7E A0 23 A1 03 BE BB AC E6 E7 00 C4 01 C1 00 02 06 04 18 00 02 1A 12 13 88 12 00 00 11 06 0F 00 09 00 13 CC 7E
System.ArgumentOutOfRangeException: Specified argument was out of the range of valid values.
at Gurux.DLMS.Objects.GXDLMSAssociationLogicalName.Gurux.DLMS.Objects.IGXDLMSBase.SetValue(GXDLMSSettings settings, ValueEventArgs e)
at Gurux.DLMS.GXDLMSClient.UpdateValue(GXDLMSObject target, Int32 attributeIndex, Object value, List`1 columns)
at Gurux.DLMS.GXDLMSClient.UpdateValue(GXDLMSObject target, Int32 attributeIndex, Object value)
at GXDLMSDirector.GXDLMSCommunicator.Read(Object sender, GXDLMSObject obj, Boolean forceRead)
at GXDLMSDirector.MainForm.Read(Object sender, GXAsyncWork work, Object[] parameters)
6:23:47 AM Send Keep Alive
7E A0 19 03 A1 1A E9 F9 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:23:47 AM
7E A0 18 A1 03 D0 24 AA E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:25:37 AM Send Keep Alive
7E A0 19 03 A1 3C DD BD E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:25:37 AM
7E A0 18 A1 03 F2 34 A8 E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:27:27 AM Send Keep Alive
7E A0 19 03 A1 5E C9 FD E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:27:27 AM
7E A0 18 A1 03 14 0C 2A E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:29:17 AM Send Keep Alive
7E A0 19 03 A1 70 B5 35 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:29:17 AM
7E A0 18 A1 03 36 1C 28 E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:31:07 AM Send Keep Alive
7E A0 19 03 A1 92 A9 F1 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:31:07 AM
7E A0 18 A1 03 58 64 A2 E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:32:57 AM Send Keep Alive
7E A0 19 03 A1 B4 9D B5 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:32:57 AM
7E A0 18 A1 03 7A 74 A0 E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
6:34:47 AM Send Keep Alive
7E A0 19 03 A1 D6 89 F5 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
6:34:47 AM
7E A0 18 A1 03 9C 4C 22 E6 E7 00 C4 01 C1 00 09 06 00 00 28 00 00 FF B6 6E 7E
2 years 9 months ago
Hi, Access rights are…
Access rights are populated when you read the object list of the current association.
Current implementation works only with DLMS standard objects, but you can modify
CGXDLMSObjectFactory::CreateObject(DLMS_OBJECT_TYPE type) to handle your custom objects.
You can check is read or read-write supported like this after you have read the association view or save that information.
if (((*it)->GetAccess(*pos) & DLMS_ACCESS_MODE_READ) != 0)
if (((*it)->GetAccess(*pos) & DLMS_ACCESS_MODE_READ_WRITE) != 0)