DLMSDirector

Currently, I am working on communication with the A1800 meter, at this moment I can connect with a low authentication and enable the DLMS /COSEM protocol in the respective meter using other software (Metercat). The problem appears when I try to interrogate a specific day or another interval of dates related to the generic profile, but the only result I have received is the following: "Access error: the device informs read-write denied.

Image
Profile picture for user Kurumi

Kurumi

7 years 9 months ago

Reading Profile generic (Elster A1800)

Hi,
Can you read all the data (Select "All" checkBox) from the Profile Generic without exception?

One problem might be date and time. Some meters expects that example millisecond is set to Zero and some expect that it's Ignored. If that is not done, meter return exception.

Can you read clock time and send it to me by email.

BR,

Mikko

deivy311

7 years 9 months ago

In reply to Reading Profile generic (Elster A1800) by Kurumi

A1800 Clock Interrogation

Hi there, again!
Thanks for your soon response, when I select "All" checkBox appear an error about the time of response and then the connection is lost.

I could not get your email, I will write the interrogation record of the clock on this channel (Time:12/20/2018 2:02:45 AM).

[20/12/2018 12:04:40] Written data (COM7)
7e a0 07 03 23 93 bf 32 7e
[20/12/2018 12:04:40] Read data (COM7)
7e a0 1e 23 03 73 7b cf 81 80 12 05 01 80 06 01
80 07 04 00 00 00 01 08 04 00 00 00 01 53 3b 7e
[20/12/2018 12:04:40] Written data (COM7)
7e a0 50 03 23 10 1b 06 e6 e6 00 60 42 a1 09 06
07 60 85 74 05 08 01 01 8a 02 07 80 8b 07 60 85
74 05 08 02 01 ac 16 80 14 12 34 56 78 20 20 20
20 20 20 20 20 20 20 20 20 20 20 20 20 be 10 04
0e 01 00 00 00 06 5f 1f 04 00 60 fe df ff ff 5c
72 7e
[20/12/2018 12:04:40] Read data (COM7)
7e a0 37 23 03 30 d4 c9 e6 e7 00 61 29 a1 09 06
07 60 85 74 05 08 01 01 a2 03 02 01 00 a3 05 a1
03 02 01 00 be 10 04 0e 08 00 06 5f 1f 04 00 00
10 1d 02 00 00 07 d8 d4 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 32 df eb e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 02 00 60 1a 7e
[20/12/2018 12:04:46] Read data (COM7)
7e a0 1e 23 03 52 f0 ff e6 e7 00 c4 01 c1 00 09
0c 07 e2 0c 14 04 0c 02 2d ff fe d4 00 bc df 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 54 ef ed e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 03 00 b8 03 7e
[20/12/2018 12:04:46] Read data (COM7)
7e a0 13 23 03 74 4b 30 e6 e7 00 c4 01 c1 00 10
fe d4 0a 72 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 76 ff ef e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 04 00 b0 4e 7e
[20/12/2018 12:04:46] Read data (COM7)
7e a0 12 23 03 96 ec e8 e6 e7 00 c4 01 c1 00 11
00 1b 4d 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 98 8f e1 e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 07 00 d8 64 7e
[20/12/2018 12:04:46] Read data (COM7)
7e a0 12 23 03 b8 90 20 e6 e7 00 c4 01 c1 00 0f
00 9a 42 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 ba 9f e3 e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 08 00 10 e7 7e
[20/12/2018 12:04:46] Read data (COM7)
7e a0 12 23 03 da 84 60 e6 e7 00 c4 01 c1 00 03
01 b3 fa 7e
[20/12/2018 12:04:46] Written data (COM7)
7e a0 19 03 23 dc af e5 e6 e6 00 c0 01 c1 00 08
00 00 01 00 00 ff 09 00 c8 fe 7e
[20/12/2018 12:04:47] Read data (COM7)
7e a0 12 23 03 fc b0 24 e6 e7 00 c4 01 c1 00 16
03 88 32 7e

On the other hand, I was able to prevent the error by changing the access right from "Buffer" to "AuthenticateRead" but the record is empty even when the result is "Ready", (by the way, the "Entries" tag is always set to 415 and this account is incremented every 15 minutes, I guess the program is reading the generic profile of all available times in the meter)

Profile picture for user Kurumi

Kurumi

7 years 9 months ago

A1800 Clock Interrogation

Hi,

Select "Advanced" tab from device settings. Check "Use UTC time zone, not standard".
Try to read 0.0.98.1.0.255 again. If it still fails, post the log.

BR,
Mikko

deivy311

7 years 9 months ago

Error with "Reading" options.

Well… I’m pleased to share the good news, when I made this change the profile generic 1 was successfully read, (only with the option “ALL” in the Reading section), Below I will share a piece of the entire reading because are many values in hex.….
(It is possible to say that analyzing other meters, I concluded that the object COSEM belonging to generic profile 1 is “1.0.99.1.0.255” and for that reason, the tests continued with this object)
[21/12/2018 10:33:28] Written data (COM7)
7e a0 19 03 23 58 83 27 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 02 00 54 89 7e
[21/12/2018 10:33:29] Read data (COM7)
7e a8 89 23 03 b4 06 9e e6 e7 00 c4 02 c1 00 00
00 00 01 00 82 01 ea 01 82 01 c3 02 06 09 0c 07
e2 0c 15 00 0a 1f 00 00 00 00 00 11 01 15 00 00
00 00 00 00 00 00 14 00 00 00 00 00 00 00 00 14
00 00 00 00 00 00 00 00 14 00 00 00 00 00 00 00
00 02 06 09 0c 07 e2 0c 15 00 0a 1e 00 00 00 00
00 11 01 15 00 00 00 00 00 00 00 00 14 00 00 00
00 00 00 00 00 14 00 00 00 00 00 00 00 00 14 00
00 00 00 00 00 00 00 02 9a 64 7e
[21/12/2018 10:33:29] Written data (COM7)
7e a0 07 03 23 71 a3 f6 7e
[21/12/2018 10:33:29] Read data (COM7)
7e a8 89 23 03 b6 14 bd 06 09 0c 07 e2 0c 15 00
0a 0f 00 00 00 00 00 11 25 15 00 00 00 00 00 00
00 00 14 00 00 00 00 00 00 00 00 14 00 00 00 00
00 00 00 00 14 00 00 00 00 00 00 00 00 02 06 09
0c 00 00 00 00 00 00 00 00 00 00 00 00 11 00 15
00 00 00 00 00 00 00 00 14 00 00 00 00 00 00 00
00 14 00 00 00 00 00 00 00 00 14 00 00 00 00 00
00 00 00 02 06 09 0c 00 00 00 00 00 00 00 00 00
00 00 00 11 00 15 00 00 ac fc 7e
[21/12/2018 10:33:29] Written data (COM7)
7e a0 07 03 23 91 ad 11 7e
[21/12/2018 10:33:29] Read data (COM7)
7e a8 89 23 03 b8 6a 54 00 00 00 00 00 00 14 00
00 00 00 00 00 00 00 14 00 00 00 00 00 00 00 00
14 00 00 00 00 00 00 00 00 02 06 09 0c 00 00 00
00 00 00 00 00 00 00 00 00 11 00 15 00 00 00 00
00 00 00 00 14 00 00 00 00 00 00 00 00 14 00 00
00 00 00 00 00 00 14 00 00 00 00 00 00 00 00 02
06 09 0c 00 00 00 00 00 00 00 00 00 00 00 00 11
00 15 00 00 00 00 00 00 00 00 14 00 00 00 00 00
00 00 00 14 00 00 00 00 70 1f 7e
[21/12/2018 10:33:29] Written data (COM7)
7e a0 07 03 23 b1 af 30 7e
[21/12/2018 10:33:30] Read data (COM7)
7e a0 82 23 03 ba 4d ed 00 00 00 00 14 00 00 00
00 00 00 00 00 02 06 09 0c 00 00 00 00 00 00 00
00 00 00 00 00 11 00 15 00 00 00 00 00 00 00 00
14 00 00 00 00 00 00 00 00 14 00 00 00 00 00 00
00 00 14 00 00 00 00 00 00 00 00 02 06 09 0c 00
00 00 00 00 00 00 00 00 00 00 00 11 00 15 00 00
00 00 00 00 00 00 14 00 00 00 00 00 00 00 00 14
00 00 00 00 00 00 00 00 14 00 00 00 00 00 00 00
00 b6 52 7e
[21/12/2018 10:33:30] Written data (COM7)
7e a0 13 03 23 da 37 5c e6 e6 00 c0 02 c1 00 00
00 01 51 be 7e
[21/12/2018 10:33:30] Read data (COM7)
7e a8 89 23 03 dc 48 71 e6 e7 00 c4 02 c1 00 00
00 00 02 00 82 01 e6 02 06 09 0c 00 00 00 00 00
00 00 00 00 00 00 00 11 00 15 00 00 00 00 00 00
00 00 14 00 00 00 00 00 00 00 00 14 00 00 00 00
00 00 00 00 14 00 00 00 00 00 00 00 00 02 06 09
0c 00 00 00 00 00 00 00 00 00 00 00 00 11 00 15
00 00 00 00 00 00 00 00 14 00 00 00 00 00 00 00
00 14 00 00 00 00 00 00 00 00 14 00 00 00 00 00
00 00 00 02 06 09 0c 00 72 f3 7e
[21/12/2018 10:33:30] Written data (COM7)
7e a0 07 03 23 f1 ab 72 7e
[21/12/2018 10:33:30] Read data (COM7)
7e a8 89 23 03 de 5a 52 00 00 00 00 00 00 00 00
00 00 00 11 00 15 00 00 00 00 00 00 00 00 14 00
00 00 00 00 00 00 00 14 00 00 00 00 00 00 00 00
14 00 00 00 00 00 00 00 00 02 06 09 0c 00 00 00
00 00 00 00 00 00 00 00 00 11 00 15 00 00 00 00
00 00 00 00 14 00 00 00 00 00 00 00 00 14 00 00
00 00 00 00 00 00 14 00 00 00 00 00 00 00 00 02
06 09 0c 00 00 00 00 00 00 00 00 00 00 00 00 11
00 15 00 00 00 00 00 00 1c b4 7e
…
The process goes on until to end successfully. However, appears another problem that is that when I wish to read a specific day and after setting this option in the "Reading" section, the meter responds with another thing, as we can see below, the program sends the next frame but with the response of meter, the “Buffer” in the “Access rights” Section is changed to “No access”. and the same occurs with the other options except "All".
[21/12/2018 10:43:38] Written data (COM7)
7e a0 4c 03 23 32 9e 50 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 02 01 01 02 04 02 04 12 00 08
09 06 00 00 01 00 00 ff 0f 02 12 00 00 09 0c 07
e2 0c 14 04 00 00 2e ff fe d4 00 09 0c 07 e2 0c
15 05 00 00 2e ff fe d4 00 01 00 55 d8 7e
[21/12/2018 10:43:39] Read data (COM7)
7e a0 11 23 03 52 09 4d e6 e7 00 c4 01 c1 01 03
73 82 7e

Profile picture for user Kurumi

Kurumi

7 years 8 months ago

Error with "Reading" options.

Hi,

Can you get any data if you select "Read last" days and change zero to example 10?

BR,

Mikko

deivy311

7 years 7 months ago

In reply to Error with "Reading" options. by Kurumi

Buffer Access Error

Hi, I've been quite busy. Well, when I try to download data about 3, 4 or 10 days ago the answer is the next:

[13/02/2019 16:58:54] Written data (COM7)
7e a0 19 03 23 32 df eb e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 04 00 84 dd 7e
[13/02/2019 16:58:55] Read data (COM7)
7e a0 15 23 03 52 e5 3f e6 e7 00 c4 01 c1 00 06
00 00 03 84 39 f0 7e
[13/02/2019 16:58:55] Written data (COM7)
7e a0 4c 03 23 54 ae 56 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 02 01 01 02 04 02 04 12 00 08
09 06 00 00 01 00 00 ff 0f 02 12 00 00 09 0c 07
e3 02 09 06 00 00 00 ff fe d4 00 09 0c 07 e3 02
0e 04 00 00 00 ff fe d4 00 01 00 e4 87 7e
[13/02/2019 16:58:55] Read data (COM7)
7e a0 11 23 03 74 3d 09 e6 e7 00 c4 01 c1 01 03
73 82 7e
[13/02/2019 16:58:55] Written data (COM7)
7e a0 19 03 23 76 ff ef e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 05 00 5c c4 7e
[13/02/2019 16:58:55] Read data (COM7)
7e a0 12 23 03 96 ec e8 e6 e7 00 c4 01 c1 00 16
02 01 23 7e
[13/02/2019 16:58:55] Written data (COM7)
7e a0 19 03 23 98 8f e1 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 06 00 34 ee 7e
[13/02/2019 16:58:55] Read data (COM7)
7e a0 22 23 03 b8 62 6c e6 e7 00 c4 01 c1 00 02
04 12 00 00 09 06 00 00 00 00 00 00 0f 00 12 00
00 7c 19 7e
[13/02/2019 16:58:55] Written data (COM7)
7e a0 19 03 23 ba 9f e3 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 07 00 ec f7 7e
[13/02/2019 16:58:55] Read data (COM7)
7e a0 15 23 03 da a5 37 e6 e7 00 c4 01 c1 00 06
00 00 02 52 5a 5a 7e
[13/02/2019 16:58:56] Written data (COM7)
7e a0 19 03 23 dc af e5 e6 e6 00 c0 01 c1 00 07
01 00 63 01 00 ff 08 00 24 74 7e
[13/02/2019 16:58:56] Read data (COM7)
7e a0 15 23 03 fc 91 73 e6 e7 00 c4 01 c1 00 06
00 00 6a 20 5a a1 7e

and in the tab, "Last errors" appears this:
Buffer
Access Error : Device reports Read-Write denied.

what could be happening?

Image
Profile picture for user Kurumi

Kurumi

7 years 7 months ago

Buffer Access Error

Hi,

Data is correct. Can you check this:
1. Select Read.Set start index to 1 and count to 3. You should receive 3 rows.
2. Select "Read From" and set start and end time to last week. End time must be something else than current date.

BR,
Mikko

  • Create new account
  • Reset your password

Hire Us!

Latest Releases

  • Wed, 08/26/2026 - 09:04
    Gurux.DLMS.Python 1.0.203
  • Mon, 08/17/2026 - 11:28
    Gurux.DLMS.Python 1.0.202
  • Mon, 08/17/2026 - 09:47
    gurux.dlms.cpp 9.0.2608.1701
  • Mon, 08/17/2026 - 09:25
    gurux.dlms.c 9.0.2608.1701
  • Mon, 07/27/2026 - 12:37
    gurux.dlms.cpp 9.0.2607.2701

New forum topics

  • Security vulnerability report — request for a private contact (GuruxDLMS.c / ANSI C)
  • Topic: Insufficient Memory Error When Reading Class 7 Profile Generic Objects
  • SN ReadResponse returns all-null values when response spans multiple HDLC frames
  • Gurux.Serial.Android 3.0.6 – CH340 (HL-340) USB-Serial Adapter Not Working,
  • Trying to talk to a L&G E360 meter (Using Python Gurux)
More

Who's new

  • cyby
  • Metin Onan
  • ssv007
  • 3nzol3dur
  • dw772
RSS feed
Privacy FAQ GXDN Issues Contact
Follow Gurux on Twitter Follow Gurux on Linkedin