Hello Mikko,
we have started with conformance tests for our meter.
I choosed the simplest configuration- Public Client with most of the tests disabled.
Conformance test resulted in failure (this was expected for the first try :-).
I would like to stop at first error- reading IC15_ATTR3 of "Current Association" object.
The meter response is "Inconsistent class".
If I read that attribute from Director, the reply is correct.
I have compared the frames and I have found, that conformance test requests Current association object as 0x15 instead of 0x0F.
Could there be a error in conformance test?
Hello Mikko,
it is misunderstanding.
The examples are two "read request IC15_ATTR3" packets.
First of them is "manual" read from Director, the second one "read during conformance tests".
The meter answers are not included (answer to the first packet is packet with correct structure, answer to conformance test request is Inconsistent class, since the client is requring class IC 21 (0x15) with obis code 0.0.40.0.0.255 which is code of IC 15 (0x0F).
The current association object clas_id is 0x0F. 0x15 is RegisterMonitor. I can't say anything with this information. Can you share the log file so I can check it? One reply doesn't help because I need to know what you have try to read.
Hello Mikko,
I have only one client- Public Client- in Gurux DLMS Director.
I connect to it. I run Refresh. I can see Association LN class with address 0.0.40.0.0.255.
I close connection.
I run Conformance Test->Run->AllDevices->OK.
The attached log is the result.
Hi Ondrej, The reason is the…
Hi Ondrej,
The reason is the client wants to read the AssociationLogicalName (0x0F) and the meter returns RegisterMonitor (0x15). The returned object is wrong.
Hello Mikko, it is…
Hello Mikko,
Best Regards
Ondrej
Hello Mikko, could You…
Hello Mikko,
could You kindly comment the case, please? I would like to move the conformance testing on.
Thank You very much.
Best Regards
Ondrej
Hi Ondrej, The current…
Hi Ondrej,
Hello Mikko, this is the…
Hello Mikko,
this is the complete log. I believe that answer to conformance test request is Inconsistent class, since the client is requring class IC 21 (0x15) with obis code 0.0.40.0.0.255 which is code of IC 15 (0x0F) (packet 15 and 16).
BR Ondrej:
BlockCipher key: 00 01 02 03 04 05 06 07 08 09 0A 0B 0C 0D 0E 0F
Authentication Key:D0 D1 D2 D3 D4 D5 D6 D7 D8 D9 DA DB DC DD DE DF
1: 7E A0 07 03 21 93 0F 01 7E
<HDLC len="9" >
<TargetAddress Value="1" />
<SourceAddress Value="10" />
<!-- SNRM frame. -->
<FrameType Value="93" />
<Snrm>
</Snrm>
</HDLC>
2: 7E A0 1E 21 03 73 C3 7A 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
<HDLC len="1D" >
<TargetAddress Value="10" />
<SourceAddress Value="1" />
<!-- UA frame. -->
<FrameType Value="73" />
<PDU>
<Ua>
<MaxInfoTX Value="128" />
<MaxInfoRX Value="128" />
<WindowSizeTX Value="1" />
<WindowSizeRX Value="1" />
</Ua>
</PDU>
</HDLC>
3: 7E A0 2B 03 21 10 FB AF E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 62 1E 5D FF FF 88 55 7E
<HDLC len="2A" >
<!-- AARQ frame. -->
<FrameType Value="10" />
<PDU>
<AssociationRequest>
<InitiateRequest>
<ProposedConformance>
<ConformanceBit Name="DeltaValueEncoding" />
<ConformanceBit Name="Get" />
<ConformanceBit Name="Set" />
</ProposedConformance>
</InitiateRequest>
</AssociationRequest>
</PDU>
</HDLC>
4: 7E A0 37 21 03 30 6C 7C E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 12 14 02 00 00 07 EA 8D 7E
<HDLC len="36" >
<!-- AARE frame. -->
<FrameType Value="30" />
<PDU>
<AssociationResponse>
<AssociationResult Value="00" />
<ResultSourceDiagnostic>
<ACSEServiceUser Value="00" />
</ResultSourceDiagnostic>
<InitiateResponse>
<NegotiatedConformance>
</NegotiatedConformance>
<NegotiatedMaxPduSize Value="0200" />
<VaaName Value="0007" />
</InitiateResponse>
</AssociationResponse>
</PDU>
</HDLC>
5: 7E A0 19 03 21 32 6F D8 E6 E6 00 C0 01 C1 00 01 00 00 2A 00 00 FF 02 00 12 80 7E
<HDLC len="18" >
<FrameType Value="32" />
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Priority: High, ServiceClass: Confirmed, Invoke ID: 1 -->
<AttributeDescriptor>
<!-- Data -->
<ClassId Value="0001" />
<!-- 0.0.42.0.0.255 -->
<InstanceId Value="00002A0000FF" />
<!-- Value -->
<AttributeId Value="02" />
</AttributeDescriptor>
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
6: 7E A0 22 21 03 52 8E 91 E6 E7 00 C4 01 C1 00 09 10 45 4C 47 30 30 30 30 30 30 30 31 32 33 34 35 36 F5 90 7E
<HDLC len="21" >
<FrameType Value="52" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<!-- ELG0000000123456 -->
<OctetString Value="454C4730303030303030313233343536" />
</Data>
</Result>
</GetResponseNormal>
</GetResponse>
</PDU>
</HDLC>
7: 7E A0 19 03 21 54 5F DE E6 E6 00 C0 01 C1 00 01 01 00 00 02 00 FF 02 00 4B BB 7E
<HDLC len="18" >
<FrameType Value="54" />
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 1.0.0.2.0.255 -->
<InstanceId Value="0100000200FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
8: 7E A0 11 21 03 74 85 BC E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<FrameType Value="74" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<DataAccessError Value="UndefinedObject" />
</Result>
</GetResponse>
</PDU>
</HDLC>
9: 7E A0 19 03 21 76 4F DC E6 E6 00 C0 01 C1 00 08 00 00 01 00 00 FF 02 00 60 1A 7E
<HDLC len="18" >
<FrameType Value="76" />
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Clock -->
<ClassId Value="0008" />
<!-- 0.0.1.0.0.255 -->
<InstanceId Value="0000010000FF" />
<!-- Time -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
10: 7E A0 11 21 03 96 99 78 E6 E7 00 C4 01 C1 01 03 73 82 7E
<HDLC len="10" >
<FrameType Value="96" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<DataAccessError Value="ReadWriteDenied" />
</Result>
</GetResponse>
</PDU>
</HDLC>
11: 7E A0 19 03 21 98 3F D2 E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 03 00 ED 51 7E
<HDLC len="18" >
<FrameType Value="98" />
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- RegisterMonitor -->
<ClassId Value="0015" />
<!-- 0.0.40.0.0.255 -->
<InstanceId Value="0000280000FF" />
<!-- Monitored Value -->
<AttributeId Value="03" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
12: 7E A0 11 21 03 B8 E5 B0 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<FrameType Value="B8" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<DataAccessError Value="InconsistentClass" />
</Result>
</GetResponse>
</PDU>
</HDLC>
13: 7E A0 19 03 21 BA 2F D0 E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 04 00 E5 1C 7E
<HDLC len="18" >
<FrameType Value="BA" />
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Actions -->
<AttributeId Value="04" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
14: 7E A0 11 21 03 DA F1 F0 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<FrameType Value="DA" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
15: 7E A0 19 03 21 DC 1F D6 E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 05 00 3D 05 7E
<HDLC len="18" >
<FrameType Value="DC" />
<PDU>
<GetRequest>
<GetRequestNormal>
<AttributeId Value="05" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
16: 7E A0 11 21 03 FC C5 B4 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<FrameType Value="FC" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
17: 7E A0 19 03 21 FE 0F D4 E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 06 00 55 2F 7E
<HDLC len="18" >
<FrameType Value="FE" />
<PDU>
<GetRequest>
<GetRequestNormal>
<AttributeId Value="06" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
18: 7E A0 11 21 03 1E D9 70 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<FrameType Value="1E" />
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
19: 7E A0 19 03 21 10 7F DA E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 08 00 45 B5 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<AttributeId Value="08" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
20: 7E A0 11 21 03 30 A5 B8 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
21: 7E A0 19 03 21 32 6F D8 E6 E6 00 C0 01 C1 00 15 00 00 28 00 00 FF 09 00 9D AC 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<AttributeId Value="09" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
22: 7E A0 11 21 03 52 B1 F8 E6 E7 00 C4 01 C1 01 09 29 2D 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
23: 7E A0 19 03 21 54 5F DE E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 03 00 4C 92 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- 0.0.40.0.16.255 -->
<InstanceId Value="0000280010FF" />
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
24: 7E A0 11 21 03 74 85 BC E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
25: 7E A0 19 03 21 76 4F DC E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 04 00 44 DF 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Actions -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
26: 7E A0 11 21 03 96 99 78 E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
27: 7E A0 19 03 21 98 3F D2 E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 05 00 9C C6 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
28: 7E A0 11 21 03 B8 E5 B0 E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
29: 7E A0 19 03 21 BA 2F D0 E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 06 00 F4 EC 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
30: 7E A0 11 21 03 DA F1 F0 E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
31: 7E A0 19 03 21 DC 1F D6 E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 08 00 E4 76 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
32: 7E A0 11 21 03 FC C5 B4 E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
33: 7E A0 19 03 21 FE 0F D4 E6 E6 00 C0 01 C1 00 15 00 00 28 00 10 FF 09 00 3C 6F 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
34: 7E A0 11 21 03 1E D9 70 E6 E7 00 C4 01 C1 01 04 CC F6 7E
<HDLC len="10" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
</Result>
</GetResponse>
</PDU>
</HDLC>
35: 7E A0 19 03 21 10 7F DA E6 E6 00 C0 01 C1 00 01 00 00 2A 00 00 FF 02 00 12 80 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
36: 7E A0 22 21 03 30 9A D1 E6 E7 00 C4 01 C1 00 09 10 45 4C 47 30 30 30 30 30 30 30 31 32 33 34 35 36 F5 90 7E
<HDLC len="21" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
37: 7E A0 19 03 21 32 6F D8 E6 E6 00 C0 01 C1 00 01 00 00 2B 01 01 FF 02 00 C6 93 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.43.1.1.255 -->
<InstanceId Value="00002B0101FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
38: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
<HDLC len="14" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<UInt32 Value="00000000" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
39: 7E A0 19 03 21 54 5F DE E6 E6 00 C0 01 C1 00 01 00 00 2B 01 03 FF 02 00 B0 AA 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.43.1.3.255 -->
<InstanceId Value="00002B0103FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
40: 7E A0 15 21 03 74 69 CE E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
<HDLC len="14" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
41: 7E A0 19 03 21 76 4F DC E6 E6 00 C0 01 C1 00 01 00 00 2B 01 30 FF 02 00 8F C3 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.43.1.48.255 -->
<InstanceId Value="00002B0130FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
42: 7E A0 15 21 03 96 75 0A E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
<HDLC len="14" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
43: 7E A0 19 03 21 98 3F D2 E6 E6 00 C0 01 C1 00 01 00 00 5E 27 1E FF 02 00 11 68 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.94.39.30.255 -->
<InstanceId Value="00005E271EFF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
44: 7E A0 1C 21 03 B8 6A 3B E6 E7 00 C4 01 C1 00 02 03 11 00 06 00 00 00 00 12 00 01 3E E9 7E
<HDLC len="1B" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<Structure Qty="03" >
<UInt8 Value="00" />
<UInt16 Value="0001" />
</Structure>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
45: 7E A0 19 03 21 BA 2F D0 E6 E6 00 C0 01 C1 00 01 00 00 60 01 00 FF 02 00 89 A0 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.96.1.0.255 -->
<InstanceId Value="0000600100FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
46: 7E A0 1A 21 03 DA E4 30 E6 E7 00 C4 01 C1 00 0A 08 30 30 31 32 33 34 35 36 C9 0C 7E
<HDLC len="19" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<String Value="00123456" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
47: 7E A0 19 03 21 DC 1F D6 E6 E6 00 C0 01 C1 00 01 00 00 60 01 03 FF 02 00 44 85 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.96.1.3.255 -->
<InstanceId Value="0000600103FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
48: 7E A0 12 21 03 FC 08 91 E6 E7 00 C4 01 C1 00 16 02 01 23 7E
<HDLC len="11" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<Enum Value="02" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
49: 7E A0 19 03 21 FE 0F D4 E6 E6 00 C0 01 C1 00 01 00 00 60 01 0A FF 02 00 27 7C 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.0.96.1.10.255 -->
<InstanceId Value="000060010AFF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
50: 7E A0 20 21 03 1E 90 20 E6 E7 00 C4 01 C1 00 0A 0E 30 30 30 30 30 30 30 30 30 30 30 30 30 30 79 EE 7E
<HDLC len="1F" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<String Value="00000000000000" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
51: 7E A0 19 03 21 10 7F DA E6 E6 00 C0 01 C1 00 01 00 01 2B 01 01 FF 02 00 13 0C 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Data -->
<!-- 0.1.43.1.1.255 -->
<InstanceId Value="00012B0101FF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
52: 7E A0 15 21 03 30 49 CA E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
<HDLC len="14" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
53: 7E A0 19 03 21 32 6F D8 E6 E6 00 C0 01 C1 00 03 00 00 5E 27 1F FF 02 00 50 EF 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Register -->
<ClassId Value="0003" />
<!-- 0.0.94.39.31.255 -->
<InstanceId Value="00005E271FFF" />
<!-- Value -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
54: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 0D FA D0 F0 7E
<HDLC len="14" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<UInt32 Value="00000DFA" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
55: 7E A0 19 03 21 54 5F DE E6 E6 00 C0 01 C1 00 03 00 00 5E 27 1F FF 03 00 88 F6 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Register -->
<!-- Scaler and Unit -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
56: 7E A0 16 21 03 74 A4 EB E6 E7 00 C4 01 C1 00 02 02 0F 00 16 07 21 59 7E
<HDLC len="15" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<Structure Qty="02" >
<Int8 Value="00" />
<Enum Value="07" />
</Structure>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
57: 7E A0 6A 03 21 76 C7 A3 E6 E6 00 C0 03 C1 09 00 01 00 00 2A 00 00 FF 02 00 00 01 00 00 2B 01 01 FF 02 00 00 01 00 00 2B 01 03 FF 02 00 00 01 00 00 2B 01 30 FF 02 00 00 01 00 00 5E 27 1E FF 02 00 00 01 00 00 60 01 00 FF 02 00 00 01 00 00 60 01 03 FF 02 00 00 01 00 00 60 01 0A FF 02 00 00 01 00 01 2B 01 01 FF 02 00 73 96 7E
<HDLC len="69" >
<PDU>
<GetRequest>
<GetRequestWithList>
<AttributeDescriptorList Qty="09" >
<AttributeDescriptorWithSelection>
<!-- Data -->
</AttributeDescriptorWithSelection>
<!-- Data -->
<!-- Data -->
<!-- Data -->
<!-- Data -->
<!-- Data -->
<!-- Data -->
<!-- Data -->
<!-- Data -->
</AttributeDescriptorList>
</GetRequestWithList>
</GetRequest>
</PDU>
</HDLC>
58: 7E A0 67 21 03 96 46 69 E6 E7 00 C4 03 C1 09 00 09 10 45 4C 47 30 30 30 30 30 30 30 31 32 33 34 35 36 00 06 00 00 00 00 00 06 00 00 00 00 00 06 00 00 00 00 00 02 03 11 00 06 00 00 00 00 12 00 01 00 0A 08 30 30 31 32 33 34 35 36 00 16 02 00 0A 0E 30 30 30 30 30 30 30 30 30 30 30 30 30 30 00 06 00 00 00 00 E6 57 7E
<HDLC len="66" >
<PDU>
<GetResponse>
<GetResponseWithList>
<Result Qty="09" >
<Data>
</Data>
<Data>
</Data>
<Data>
</Data>
<Data>
</Data>
<Data>
</Structure>
</Data>
<Data>
</Data>
<Data>
<Enum Value="02" />
</Data>
<Data>
</Data>
<Data>
</Data>
</Result>
</GetResponseWithList>
</GetResponse>
</PDU>
</HDLC>
59: 7E A0 19 03 21 98 3F D2 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 04 00 41 07 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- AssociationLogicalName -->
<ClassId Value="000F" />
<!-- Application Context Name -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
60: 7E A0 19 21 03 B8 3D 55 E6 E7 00 C4 01 C1 00 09 07 60 85 74 05 08 01 01 E2 49 7E
<HDLC len="18" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<OctetString Value="60857405080101" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
61: 7E A0 19 03 21 BA 2F D0 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 05 00 99 1E 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- xDLMS Context Info -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
62: 7E A0 23 21 03 DA 75 85 E6 E7 00 C4 01 C1 00 02 06 04 18 00 12 14 12 02 00 12 01 F8 11 06 0F 00 09 00 4B 0D 7E
<HDLC len="22" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<Structure Qty="06" >
<BitString Value="000000000001001000010100" />
<UInt16 Value="0200" />
<UInt16 Value="01F8" />
<UInt8 Value="06" />
<Int8 Value="00" />
<OctetString Value="" />
</Structure>
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
63: 7E A0 19 03 21 DC 1F D6 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 06 00 F1 34 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Authentication Mechanism Name -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
64: 7E A0 19 21 03 FC 1D 51 E6 E7 00 C4 01 C1 00 09 07 60 85 74 05 08 02 00 03 72 7E
<HDLC len="18" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<OctetString Value="60857405080200" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
65: 7E A0 19 03 21 FE 0F D4 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 08 00 E1 AE 7E
<HDLC len="18" >
<PDU>
<GetRequest>
<GetRequestNormal>
<!-- Association Status -->
</GetRequestNormal>
</GetRequest>
</PDU>
</HDLC>
66: 7E A0 12 21 03 1E 14 55 E6 E7 00 C4 01 C1 00 16 02 01 23 7E
<HDLC len="11" >
<PDU>
<GetResponse>
<GetResponseNormal>
<Result>
<Data>
<Enum Value="02" />
</Data>
</Result>
</GetResponse>
</PDU>
</HDLC>
67: 7E A0 07 03 21 53 03 C7 7E
<HDLC len="9" >
<!-- Disconnect Request frame. -->
<FrameType Value="53" />
<DisconnectRequest>
</DisconnectRequest>
</HDLC>
68: 7E A0 1E 21 03 73 C3 7A 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
<HDLC len="1D" >
<!-- UA frame. -->
<PDU>
<Ua>
</Ua>
</PDU>
</HDLC>
Hi Ondrej, There are lots of…
Hi Ondrej,
There are lots of inconsistent class errors. You try to read objects that don't exists.
Try to read the association view again selecting "Refresh" from the "File" menu.
I believe that you have read this association from a different meter or using a different authentication level.
Hello Mikko, I have only one…
Hello Mikko,
I close connection.
BR Ondrej
Hi Ondrej, I'm sorry for…
Hi Ondrej,
I'm sorry for slow reply. There were some problems and I didn't notified from your email.
https://gurux.fi/forum-issue
This is now fixed. Get the latest version (9.0.2303.2301) from the GXDLMSDirector.
Hello Mikko, no problem, I…
Hello Mikko,
no problem, I confirm that the issue is fixed.
Thank You.
Best Regards
Ondrej