  3. ‘FrameType’ and TX/RX Issues In The 'Collecting Objects' Step
‘FrameType’ and TX/RX issues in the 'Collecting objects' step
By Laura Chu , 30 December, 2021
Dear administrator,
In the 'Collecting objects' step, I found two issues:
The first one is that the ‘FrameType’ in the HDLC frame seems to be incorrect. The frame is as follows:
16:44:59
TX: 7E A0 77 00 20 00 23 03 54 32 9A E6 E6 00 C0 03 C1 0A 00 03 01 00 00 06
00 FF 03 00 00 03 01 00 00 06 01 FF 03 00 00 03 01 00 00 06 02 FF 03 00 00 03
01 00 00 06 03 FF 03 00 00 04 01 00 01 02 00 FF 03 00 00 04 01 00 01 02 01 FF
03 00 00 04 01 00 01 02 02 FF 03 00 00 04 01 00 01 02 03 FF 03 00 00 04 01 00
01 02 04 FF 03 00 00 05 01 00 01 04 00 FF 04 00 73 9D 7E
16:44:59
RX: 7E A0 21 03 00 20 00 23 74 E1 BD E6 E7 00 C4 02 C1 00 00 00 00 01 00 08
0A 00 02 02 0F FF 16 23 C7 AE 7E
16:44:59
TX: 7E A0 16 00 20 00 23 03 BA 12 AF E6 E6 00 C0 02 C1 00 00 00 01 51 BE 7E
16:44:59
RX: 7E A0 0A 03 00 20 00 23 71 4D FF 7E
Please note that the ‘FrameType’ in the first TX frame is 0x54, but the ‘FrameType’ in the second TX frame is 0xBA, the 'S' and 'R' of the TX frame seem to be incorrect.
The second issue is that after the first issue, Gurux cannot send and receive data correctly. The frame is as follows:
GURUX:
16:45:00
TX: 7E A0 16 00 20 00 23 03 76 72 A3 E6 E6 00 C0 02 C1 00 00 00 07 67 DB 7E
16:45:05 Data send failed. Try to resend 1/3 7E A0 1A 03 00 20 00 23 96 35 D9
E6 E7 00 C4 02 C1 02 00 00 00 02 01 0F 00 9B 14 7E
16:45:05
RX: 7E A0 1A 03 00 20 00 23 96 35 D9 E6 E7 00 C4 02 C1 02 00 00 00 02 01 0F
00 9B 14 7E 7E A0 0A 03 00 20 00 23 91 43 18 7E However, I use the serial port monitoring tool to find that the data sent and received are correct, and the frame is as follows:
16:45:00 WRITE COM1
16:45:00 READ COM1
7E A0 1A 03 00 20 00 23 96 35 D9 E6 E7 00 C4 02 C1 02 00 00 00 02 01 0F 00 9B
14 7E
16:45:04 WRITE COM1
16:45:04 READ COM1
Sorry for my English and look forward to your reply.
4 years 10 months ago
Have you modified the source code? HDLC frame issue looks odd. What programming language you are using?
Laura Chu
I use the 'Gurux GXDLMSDirector', version is '8.2.2112.2101'. I just used GURUX to get the meter data, did not modify the source code.
Can you add the entire log file so I can check what is happening?
Laura Chu
The log is as follows:
16:45:55 Collecting objects
TX: 7E A0 1C 00 20 00 23 03 32 05 4E E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 02 00 91 53 7E
16:45:55
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 01 00 81 D1 01 82 01 B0 02 04 12 00 09 11 00 09 06 00 00 0A 00 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 00 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 00 64 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 F6 13 7E
16:45:55
TX: 7E A0 0A 00 20 00 23 03 51 9C F2 7E
16:45:55
RX: 7E A0 6B 03 00 20 00 23 54 B2 B2 0F 02 16 03 00 01 01 02 02 0F 01 16 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 6B FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 01 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 F5 87 7E
16:45:55
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 01 51 BE 7E
16:45:56
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 02 00 81 CD 02 04 12 00 09 11 00 09 06 00 00 0A 02 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 03 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 04 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 EE 8B 7E
16:45:56
TX: 7E A0 0A 00 20 00 23 03 91 90 34 7E
16:45:56
RX: 7E A0 67 03 00 20 00 23 78 46 E8 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 05 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 06 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 00 01 01 02 02 0F 01 16 01 8D 6E 7E
16:45:56
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 02 CA 8C 7E
16:45:56
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 03 00 81 D3 02 04 12 00 0B 11 00 09 06 00 00 0B 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 14 11 00 09 06 00 00 0D 00 00 FF 02 02 01 0A 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 45 8D 7E
16:45:56
TX: 7E A0 0A 00 20 00 23 03 D1 94 76 7E
16:45:56
RX: 7E A0 6D 03 00 20 00 23 9C 3B A0 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 02 03 0F 0A 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 06 11 00 09 06 00 00 0E 00 01 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 01 03 02 02 0F 01 16 00 02 02 0F 02 16 00 02 02 0F 03 16 00 D9 BF 7E
16:45:56
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 03 43 9D 7E
16:45:57
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 04 00 81 CD 02 04 12 00 06 11 00 09 06 00 00 0E 00 02 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 01 03 02 02 0F 01 16 00 02 02 0F 02 16 00 02 02 0F 03 16 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 02 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 8F 68 7E
16:45:57
TX: 7E A0 0A 00 20 00 23 03 11 98 B0 7E
16:45:57
RX: 7E A0 67 03 00 20 00 23 B0 02 A2 01 00 02 04 12 00 07 11 01 09 06 00 00 15 00 01 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 00 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 00 00 02 03 0F 06 16 00 00 02 03 0F 07 16 00 00 02 03 0F 08 16 00 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 20 0C 7E
16:45:57
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 04 FC E9 7E
16:45:57
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 05 00 81 D5 02 04 12 00 07 11 01 09 06 00 00 15 00 02 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 00 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 00 00 02 03 0F 06 16 00 00 02 03 0F 07 16 00 00 02 03 0F 08 16 00 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 07 11 01 09 06 00 00 15 00 03 FF 02 02 01 08 02 03 0F 01 16 01 63 1B 7E
16:45:57
16:45:58
RX: 7E A0 6F 03 00 20 00 23 D4 CC 59 00 02 03 0F 02 16 00 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 00 00 02 03 0F 06 16 00 00 02 03 0F 07 16 00 00 02 03 0F 08 16 00 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 01 11 00 09 06 00 00 2A 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 D5 35 7E
16:45:58
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 05 75 F8 7E
16:45:58
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 06 00 81 BC 02 04 12 00 12 11 00 09 06 00 00 2C 00 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 03 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 01 04 02 02 0F 01 16 01 02 02 0F 02 16 01 02 02 0F 03 16 01 02 02 0F 04 16 01 02 04 12 00 12 11 00 09 06 00 00 2C 00 01 FF 02 02 01 07 02 35 B1 7E
16:45:58
16:45:58
RX: 7E A0 56 03 00 20 00 23 F8 D1 25 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 03 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 01 04 02 02 0F 01 16 01 02 02 0F 02 16 01 02 02 0F 03 16 01 02 02 0F 04 16 01 FE BF 7E
16:45:58
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 06 EE CA 7E
16:45:58
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 07 00 81 C7 02 04 12 00 12 11 00 09 06 00 00 2C 00 02 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 03 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 01 04 02 02 0F 01 16 01 02 02 0F 02 16 01 02 02 0F 03 16 01 02 02 0F 04 16 01 02 04 12 00 01 11 00 09 06 00 00 60 01 00 FF 02 02 01 02 02 DB 50 7E
16:45:58
16:45:59
RX: 7E A0 61 03 00 20 00 23 1C A9 95 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 C0 2E 7E
16:45:59
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 07 67 DB 7E
16:45:59
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 08 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 01 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 04 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 06 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 C4 34 7E
16:45:59
16:45:59
RX: 7E A0 6C 03 00 20 00 23 30 88 50 00 00 60 01 09 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0A 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0A 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 F6 3A 7E
16:45:59
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 08 90 23 7E
16:45:59
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 09 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 32 0A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 0B FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 0C FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 C5 EC 7E
16:45:59
16:46:00
RX: 7E A0 6C 03 00 20 00 23 54 AA 75 00 00 60 32 0D FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 0F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 11 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 AD CB 7E
16:46:00
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 09 19 32 7E
16:46:00
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 0A 00 81 AF 02 04 12 00 01 11 00 09 06 00 00 60 32 12 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 2E FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 32 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 42 E2 7E
16:46:00
16:46:00
RX: 7E A0 49 03 00 20 00 23 78 E4 0D 00 00 60 33 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 33 04 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 19 69 7E
16:46:00
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 0A 82 00 7E
16:46:01
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 0B 00 81 E5 02 04 12 00 07 11 01 09 06 00 00 60 33 05 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 00 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 00 00 02 03 0F 06 16 00 00 02 03 0F 07 16 00 00 02 03 0F 08 16 00 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 01 11 00 09 06 00 00 60 33 06 FF 02 02 01 02 02 03 0F 01 16 01 6A A2 7E
16:46:01
16:46:01
RX: 7E A0 7F 03 00 20 00 23 9C 49 22 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 35 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 E5 10 7E
16:46:01
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 0B 0B 11 7E
16:46:01
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 0C 00 81 E5 02 04 12 00 01 11 00 09 06 00 00 61 61 04 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 1E 26 7E
16:46:01
16:46:01
RX: 7E A0 7F 03 00 20 00 23 B0 27 C9 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 01 11 00 09 06 01 00 00 02 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 08 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 A0 49 7E
16:46:01
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 0C B4 65 7E
16:46:02
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 0D 00 81 E3 02 04 12 00 01 11 00 09 06 01 00 00 03 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 00 06 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 00 06 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 30 A6 7E
16:46:02
16:46:02
RX: 7E A0 7D 03 00 20 00 23 D4 BE DB 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 00 06 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 00 06 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 7A 12 7E
16:46:02
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 0D 3D 74 7E
16:46:02
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 0E 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 01 02 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 E0 45 7E
16:46:02
16:46:02
RX: 7E A0 54 03 00 20 00 23 F8 6A 12 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 EA A3 7E
16:46:02
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 0E A6 46 7E
16:46:03
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 0F 00 81 DC 02 04 12 00 04 11 00 09 06 01 00 01 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 13 66 7E
16:46:03
16:46:03
RX: 7E A0 76 03 00 20 00 23 1C 78 E7 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 01 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 00 13 7E
16:46:03
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 0F 2F 57 7E
16:46:03
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 10 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 01 04 01 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 01 04 02 FF 02 02 01 D1 F2 7E
16:46:03
16:46:04
RX: 7E A0 5A 03 00 20 00 23 30 0F DE 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 F1 26 7E
16:46:04
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 10 59 BF 7E
16:46:04
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 11 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 01 04 03 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 01 04 04 FF 02 02 01 0B B7 7E
16:46:04
16:46:04
RX: 7E A0 5A 03 00 20 00 23 54 2D FB 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 F1 26 7E
16:46:04
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 11 D0 AE 7E
16:46:04
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 12 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 01 05 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 1F C5 7E
16:46:04
16:46:05
RX: 7E A0 54 03 00 20 00 23 78 62 96 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 72 56 7E
16:46:05
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 12 4B 9C 7E
16:46:05
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 13 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 01 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 70 DF 7E
16:46:05
16:46:05
RX: 7E A0 54 03 00 20 00 23 9C 48 37 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 AD 53 7E
16:46:05
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 13 C2 8D 7E
16:46:05
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 14 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 01 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 8E 0A 7E
16:46:05
16:46:06
RX: 7E A0 54 03 00 20 00 23 B0 26 DC 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 01 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 0C 3E 7E
16:46:06
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 14 7D F9 7E
16:46:06
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 15 00 81 CE 02 04 12 00 04 11 00 09 06 01 00 01 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 01 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 24 AA 7E
16:46:06
16:46:06
RX: 7E A0 68 03 00 20 00 23 D4 D4 9E 03 11 00 09 06 01 00 01 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 01 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 56 41 7E
16:46:06
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 15 F4 E8 7E
16:46:07
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 16 00 81 DC 02 04 12 00 03 11 00 09 06 01 00 01 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 01 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 02 00 FF 02 02 01 C7 FB 7E
16:46:07
16:46:07
RX: 7E A0 76 03 00 20 00 23 F8 52 46 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 1F 75 7E
16:46:07
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 16 6F DA 7E
16:46:07
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 17 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 02 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 D3 84 7E
16:46:07
16:46:07
RX: 7E A0 54 03 00 20 00 23 1C 40 B3 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 6C 76 7E
16:46:07
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 17 E6 CB 7E
16:46:08
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 18 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 02 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 02 04 01 FF 02 02 01 DA B2 7E
16:46:08
16:46:08
16:46:08
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 18 11 33 7E
16:46:08
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 19 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 02 04 02 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 02 04 03 FF 02 02 01 10 DA 7E
16:46:08
16:46:08
16:46:08
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 19 98 22 7E
16:46:09
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 1A 00 81 DC 02 04 12 00 05 11 00 09 06 01 00 02 04 04 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 04 11 00 09 06 01 00 02 05 00 FF 02 02 01 CA AE 7E
16:46:09
16:46:09
RX: 7E A0 76 03 00 20 00 23 78 5A C2 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 87 80 7E
16:46:09
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 1A 03 10 7E
16:46:09
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 1B 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 02 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 2A 7D 7E
16:46:09
16:46:09
RX: 7E A0 54 03 00 20 00 23 9C 48 37 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 F4 83 7E
16:46:09
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 1B 8A 01 7E
16:46:10
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 1C 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 02 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 7D 8B 7E
16:46:10
16:46:10
RX: 7E A0 54 03 00 20 00 23 B0 26 DC 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 58 EC 7E
16:46:10
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 1C 35 75 7E
16:46:10
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 1D 00 81 DC 02 04 12 00 04 11 00 09 06 01 00 02 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 02 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 8E A8 7E
16:46:10
16:46:10
RX: 7E A0 76 03 00 20 00 23 D4 3C AD 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 02 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 02 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 55 A0 7E
16:46:10
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 1D BC 64 7E
16:46:11
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 1E 00 81 CE 02 04 12 00 03 11 00 09 06 01 00 02 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 02 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 02 08 04 FF 02 02 01 43 33 7E
16:46:11
16:46:11
RX: 7E A0 68 03 00 20 00 23 F8 BA 75 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 02 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 C4 E1 7E
16:46:11
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 1E 27 56 7E
16:46:11
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 1F 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 03 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 17 38 7E
16:46:11
16:46:12
RX: 7E A0 54 03 00 20 00 23 1C 40 B3 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 74 7E
16:46:12
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 1F AE 47 7E
16:46:12
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 20 00 81 9E 02 04 12 00 04 11 00 09 06 01 00 03 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 03 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 18 16 7E
16:46:12
16:46:12
RX: 7E A0 38 03 00 20 00 23 30 31 4D 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 98 74 7E
16:46:12
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 20 DA 8E 7E
16:46:12
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 21 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 03 04 01 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 03 04 02 FF 02 02 01 76 AD 7E
16:46:12
16:46:13
16:46:13
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 21 53 9F 7E
16:46:13
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 22 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 03 04 03 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 03 04 04 FF 02 02 01 80 21 7E
16:46:13
16:46:13
RX: 7E A0 5A 03 00 20 00 23 78 43 10 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 F1 26 7E
16:46:13
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 22 C8 AD 7E
16:46:13
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 23 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 03 05 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 BC 98 7E
16:46:13
16:46:14
RX: 7E A0 54 03 00 20 00 23 9C 48 37 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 0A 5D 7E
16:46:14
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 23 41 BC 7E
16:46:14
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 24 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 03 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 B6 D1 7E
16:46:14
16:46:14
RX: 7E A0 54 03 00 20 00 23 B0 26 DC 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 D5 58 7E
16:46:14
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 24 FE C8 7E
16:46:14
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 25 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 03 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 2D 57 7E
16:46:14
16:46:15
RX: 7E A0 54 03 00 20 00 23 D4 04 F9 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 03 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 74 35 7E
16:46:15
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 25 77 D9 7E
16:46:15
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 26 00 81 CE 02 04 12 00 04 11 00 09 06 01 00 03 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 03 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 AB 3E 7E
16:46:15
16:46:15
RX: 7E A0 68 03 00 20 00 23 F8 BA 75 03 11 00 09 06 01 00 03 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 03 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 37 F8 7E
16:46:15
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 26 EC EB 7E
16:46:15
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 27 00 81 DC 02 04 12 00 03 11 00 09 06 01 00 03 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 03 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 02 00 FF 02 02 01 2D 5D 7E
16:46:15
16:46:16
RX: 7E A0 76 03 00 20 00 23 1C 78 E7 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 97 68 7E
16:46:16
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 27 65 FA 7E
16:46:16
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 28 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 04 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 F9 DA 7E
16:46:16
16:46:16
RX: 7E A0 54 03 00 20 00 23 30 2E 58 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 E4 6B 7E
16:46:16
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 28 92 02 7E
16:46:17
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 29 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 04 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 04 04 01 FF 02 02 01 1A 85 7E
16:46:17
16:46:17
16:46:17
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 29 1B 13 7E
16:46:17
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 2A 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 04 04 02 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 04 04 03 FF 02 02 01 FC 24 7E
16:46:17
16:46:17
16:46:17
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 2A 80 21 7E
16:46:18
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 2B 00 81 DC 02 04 12 00 05 11 00 09 06 01 00 04 04 04 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 04 11 00 09 06 01 00 04 05 00 FF 02 02 01 0A 99 7E
16:46:18
16:46:18
RX: 7E A0 76 03 00 20 00 23 9C 70 63 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 0F 9D 7E
16:46:18
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 2B 09 30 7E
16:46:18
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 2C 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 04 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 83 1F 7E
16:46:18
16:46:18
RX: 7E A0 54 03 00 20 00 23 B0 26 DC 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 7C 9E 7E
16:46:18
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 2C B6 44 7E
16:46:19
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 2D 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 04 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 B1 BA 7E
16:46:19
16:46:19
RX: 7E A0 54 03 00 20 00 23 D4 04 F9 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 D0 F1 7E
16:46:19
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 2D 3F 55 7E
16:46:19
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 2E 00 81 DC 02 04 12 00 04 11 00 09 06 01 00 04 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 04 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 6E 50 7E
16:46:19
16:46:20
RX: 7E A0 76 03 00 20 00 23 F8 52 46 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 04 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 04 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 E7 63 7E
16:46:20
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 2E A4 67 7E
16:46:20
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 2F 00 81 CE 02 04 12 00 03 11 00 09 06 01 00 04 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 04 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 04 08 04 FF 02 02 01 DF B6 7E
16:46:20
16:46:20
RX: 7E A0 68 03 00 20 00 23 1C 90 D4 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 02 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 4C FC 7E
16:46:20
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 2F 2D 76 7E
16:46:20
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 30 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 05 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 3B 1F 7E
16:46:20
16:46:21
RX: 7E A0 54 03 00 20 00 23 30 2E 58 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 8A 69 7E
16:46:21
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 30 5B 9E 7E
16:46:21
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 31 00 81 9E 02 04 12 00 04 11 00 09 06 01 00 05 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 05 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 D8 D5 7E
16:46:21
16:46:21
RX: 7E A0 38 03 00 20 00 23 54 13 68 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 98 74 7E
16:46:21
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 31 D2 8F 7E
16:46:21
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 32 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 05 04 01 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 05 04 02 FF 02 02 01 96 A1 7E
16:46:21
16:46:22
16:46:22
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 32 49 BD 7E
16:46:22
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 33 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 05 04 03 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 05 04 04 FF 02 02 01 4C E4 7E
16:46:22
16:46:22
RX: 7E A0 5A 03 00 20 00 23 9C 69 B1 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 F1 26 7E
16:46:22
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 33 C0 AC 7E
16:46:22
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 34 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 05 05 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 19 08 7E
16:46:22
16:46:23
RX: 7E A0 54 03 00 20 00 23 B0 26 DC 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 82 40 7E
16:46:23
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 34 7F D8 7E
16:46:23
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 35 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 05 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 76 12 7E
16:46:23
16:46:23
RX: 7E A0 54 03 00 20 00 23 D4 04 F9 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 5D 45 7E
16:46:23
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 35 F6 C9 7E
16:46:24
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 36 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 05 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 C1 5D 7E
16:46:24
16:46:24
RX: 7E A0 54 03 00 20 00 23 F8 6A 12 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 05 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 FC 28 7E
16:46:24
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 36 6D FB 7E
16:46:24
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 37 00 81 CE 02 04 12 00 04 11 00 09 06 01 00 05 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 05 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 6B FD 7E
16:46:24
16:46:24
RX: 7E A0 68 03 00 20 00 23 1C 90 D4 03 11 00 09 06 01 00 05 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 05 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 85 3B 7E
16:46:24
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 37 E4 EA 7E
16:46:25
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 38 00 81 DC 02 04 12 00 03 11 00 09 06 01 00 05 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 05 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 02 00 FF 02 02 01 2D 2A 7E
16:46:25
16:46:25
RX: 7E A0 76 03 00 20 00 23 30 16 0C 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 EF 63 7E
16:46:25
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 38 13 12 7E
16:46:25
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 39 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 06 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 56 75 7E
16:46:25
16:46:25
RX: 7E A0 54 03 00 20 00 23 54 0C 7D 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 9C 60 7E
16:46:25
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 39 9A 03 7E
16:46:26
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 3A 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 06 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 06 04 01 FF 02 02 01 9D E1 7E
16:46:26
16:46:26
16:46:26
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 3A 01 31 7E
16:46:26
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 3B 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 06 04 02 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 06 04 03 FF 02 02 01 57 89 7E
16:46:26
16:46:26
16:46:26
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 3B 88 20 7E
16:46:27
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 3C 00 81 DC 02 04 12 00 05 11 00 09 06 01 00 06 04 04 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 04 11 00 09 06 01 00 06 05 00 FF 02 02 01 C4 67 7E
16:46:27
16:46:27
RX: 7E A0 76 03 00 20 00 23 B0 1E 88 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 77 96 7E
16:46:27
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 3C 37 54 7E
16:46:27
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 3D 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 06 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 2C B0 7E
16:46:27
16:46:28
RX: 7E A0 54 03 00 20 00 23 D4 04 F9 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 04 95 7E
16:46:28
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 3D BE 45 7E
16:46:28
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 3E 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 06 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 32 DC 7E
16:46:28
16:46:28
RX: 7E A0 54 03 00 20 00 23 F8 6A 12 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 A8 FA 7E
16:46:28
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 3E 25 77 7E
16:46:28
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 3F 00 81 DC 02 04 12 00 04 11 00 09 06 01 00 06 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 06 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 C1 FF 7E
16:46:28
16:46:29
RX: 7E A0 76 03 00 20 00 23 1C 78 E7 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 06 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 06 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 86 DA 7E
16:46:29
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 3F AC 66 7E
16:46:29
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 40 00 81 CE 02 04 12 00 03 11 00 09 06 01 00 06 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 06 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 06 08 04 FF 02 02 01 AA 85 7E
16:46:29
16:46:29
RX: 7E A0 68 03 00 20 00 23 30 FE 3F 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 02 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 34 F7 7E
16:46:29
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 40 DC ED 7E
16:46:30
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 41 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 07 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 91 AE 7E
16:46:30
16:46:30
RX: 7E A0 54 03 00 20 00 23 54 0C 7D 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 F2 62 7E
16:46:30
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 41 55 FC 7E
16:46:30
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 42 00 81 9E 02 04 12 00 04 11 00 09 06 01 00 07 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 07 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 5E AD 7E
16:46:30
16:46:30
RX: 7E A0 38 03 00 20 00 23 78 7D 83 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 98 74 7E
16:46:30
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 42 CE CE 7E
16:46:31
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 43 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 07 04 01 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 07 04 02 FF 02 02 01 38 12 7E
16:46:31
16:46:31
16:46:31
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 43 47 DF 7E
16:46:31
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 44 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 07 04 03 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 07 04 04 FF 02 02 01 87 04 7E
16:46:31
16:46:31
RX: 7E A0 5A 03 00 20 00 23 B0 07 5A 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 F1 26 7E
16:46:31
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 44 F8 AB 7E
16:46:32
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 45 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 07 05 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 B3 B9 7E
16:46:32
16:46:32
RX: 7E A0 54 03 00 20 00 23 D4 04 F9 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 FA 4B 7E
16:46:32
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 45 71 BA 7E
16:46:32
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 46 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 07 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 F0 6A 7E
16:46:32
16:46:32
RX: 7E A0 54 03 00 20 00 23 F8 6A 12 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 25 4E 7E
16:46:32
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 46 EA 88 7E
16:46:33
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 47 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 07 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 6B EC 7E
16:46:33
16:46:33
RX: 7E A0 54 03 00 20 00 23 1C 40 B3 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 07 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 84 23 7E
16:46:33
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 47 63 99 7E
16:46:33
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 48 00 81 CE 02 04 12 00 04 11 00 09 06 01 00 07 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 07 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 27 23 7E
16:46:33
16:46:33
RX: 7E A0 68 03 00 20 00 23 30 FE 3F 03 11 00 09 06 01 00 07 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 07 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 E4 82 7E
16:46:33
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 48 94 61 7E
16:46:34
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 49 00 81 DC 02 04 12 00 03 11 00 09 06 01 00 07 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 07 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 02 00 FF 02 02 01 22 BE 7E
16:46:34
16:46:34
RX: 7E A0 76 03 00 20 00 23 54 34 29 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 02 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 87 53 7E
16:46:34
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 49 1D 70 7E
16:46:34
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 4A 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 08 02 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 02 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 61 B9 7E
16:46:34
16:46:34
RX: 7E A0 54 03 00 20 00 23 78 62 96 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 02 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 F4 50 7E
16:46:34
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 4A 86 42 7E
16:46:35
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 4B 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 08 04 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 08 04 01 FF 02 02 01 9A EA 7E
16:46:35
16:46:35
16:46:35
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 4B 0F 53 7E
16:46:35
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 4C 00 81 C0 02 04 12 00 05 11 00 09 06 01 00 08 04 02 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 05 11 00 09 06 01 00 08 04 03 FF 02 02 01 35 D1 7E
16:46:35
16:46:36
16:46:36
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 4C B0 27 7E
16:46:36
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 4D 00 81 DC 02 04 12 00 05 11 00 09 06 01 00 08 04 04 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 04 11 00 09 06 01 00 08 05 00 FF 02 02 01 C3 6C 7E
16:46:36
TX: 7E A0 0A 00 20 00 23 03 51 9C F2 7E
16:46:36
RX: 7E A0 76 03 00 20 00 23 D4 3C AD 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 05 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 1F A6 7E
16:46:36
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 4D 39 36 7E
16:46:36
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 4E 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 08 05 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 05 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 1B 7C 7E
16:46:36
TX: 7E A0 0A 00 20 00 23 03 91 90 34 7E
16:46:37
RX: 7E A0 54 03 00 20 00 23 F8 6A 12 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 05 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 6C A5 7E
16:46:37
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 4E A2 04 7E
16:46:37
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 4F 00 81 BA 02 04 12 00 04 11 00 09 06 01 00 08 06 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 06 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 29 D9 7E
16:46:37
TX: 7E A0 0A 00 20 00 23 03 D1 94 76 7E
16:46:37
RX: 7E A0 54 03 00 20 00 23 1C 40 B3 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 06 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 C0 CA 7E
16:46:37
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 4F 2B 15 7E
16:46:38
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 50 00 81 DC 02 04 12 00 04 11 00 09 06 01 00 08 06 03 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 04 11 00 09 06 01 00 08 06 04 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 3A EC 7E
16:46:38
TX: 7E A0 0A 00 20 00 23 03 11 98 B0 7E
16:46:38
RX: 7E A0 76 03 00 20 00 23 30 16 0C 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 08 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 08 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 92 EC 7E
16:46:38
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 50 5D FD 7E
16:46:38
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 51 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 08 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 08 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 08 08 04 FF 02 02 01 BA A6 7E
16:46:38
16:46:38
RX: 7E A0 5A 03 00 20 00 23 54 2D FB 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0F 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 53 3D 7E
16:46:38
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 51 D4 EC 7E
16:46:39
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 52 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 0F 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0F 08 02 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0F 08 03 FF 02 02 01 01 91 7E
16:46:39
16:46:39
RX: 7E A0 5A 03 00 20 00 23 78 43 10 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0F 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 B7 09 7E
16:46:39
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 52 4F DE 7E
16:46:39
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 53 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 10 08 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 10 08 01 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 10 08 02 FF 02 02 01 1C 6E 7E
16:46:39
16:46:39
RX: 7E A0 5A 03 00 20 00 23 9C 69 B1 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 10 08 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 50 12 7E
16:46:39
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 53 C6 CF 7E
16:46:40
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 54 00 81 E2 02 04 12 00 03 11 00 09 06 01 00 10 08 04 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 07 11 01 09 06 01 00 63 01 00 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 30 89 7E
16:46:40
16:46:40
RX: 7E A0 7C 03 00 20 00 23 B0 49 61 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 07 11 01 09 06 01 00 63 02 00 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 3D 80 7E
16:46:40
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 54 79 BB 7E
16:46:40
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 55 00 81 E1 02 04 12 00 01 11 00 09 06 01 01 00 02 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 01 00 02 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 01 00 02 08 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 08 11 00 09 06 30 88 7E
16:46:40
16:46:41
RX: 7E A0 7B 03 00 20 00 23 D4 73 83 00 00 01 00 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 01 00 01 06 02 02 0F 01 16 00 02 02 0F 02 16 00 02 02 0F 03 16 00 02 02 0F 04 16 00 02 02 0F 05 16 00 02 02 0F 06 16 00 DE FC 7E
16:46:41
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 55 F0 AA 7E
16:46:41
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 56 00 81 DE 02 04 12 00 1B 11 01 09 06 00 00 02 00 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 1D 11 02 09 06 00 00 02 01 00 FF 02 02 01 06 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 01 01 02 02 19 60 7E
16:46:41
16:46:41
RX: 7E A0 78 03 00 20 00 23 F8 73 C0 0F 01 16 01 02 04 12 00 1C 11 00 09 06 00 00 02 02 00 FF 02 02 01 06 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 67 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 00 87 E9 7E
16:46:41
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 56 6B 98 7E
16:46:42
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 57 00 81 DD 02 04 12 00 09 11 00 09 06 00 00 0A 00 6A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 6C FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 01 02 04 12 00 09 11 00 09 06 00 00 0A 07 00 FF 02 02 01 02 02 03 0F 01 16 00 00 02 03 0F 02 16 00 C9 D3 7E
16:46:42
16:46:42
RX: 7E A0 77 03 00 20 00 23 1C AD 78 00 01 01 02 02 0F 01 16 01 02 04 12 00 16 11 00 09 06 00 00 0F 00 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 01 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 6F 9E 7E
16:46:42
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 57 E2 89 7E
16:46:42
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 58 00 81 93 02 04 12 00 16 11 00 09 06 00 00 0F 00 03 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 15 11 00 09 06 00 00 10 01 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 15 11 00 09 06 00 00 10 01 01 FF 02 02 BC 7E
16:46:42
16:46:42
RX: 7E A0 2D 03 00 20 00 23 30 5B 08 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 47 CC 7E
16:46:42
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 58 15 71 7E
16:46:43
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 59 00 81 B6 02 04 12 00 47 11 00 09 06 00 00 11 00 00 FF 02 02 01 0B 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 02 03 0F 0A 16 01 00 02 03 0F 0B 16 01 00 01 00 02 04 12 00 13 11 01 09 06 00 00 14 00 00 FF 02 F4 8B 7E
16:46:43
16:46:43
RX: 7E A0 50 03 00 20 00 23 54 7A 12 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 02 00 02 03 0F 08 16 02 00 02 03 0F 09 16 02 00 01 00 61 46 7E
16:46:43
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 59 9C 60 7E
16:46:43
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 5A 00 81 93 02 04 12 00 17 11 01 09 06 00 00 16 00 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 00 02 04 12 00 29 11 00 09 06 00 00 19 00 00 FF 02 02 01 06 02 03 0F 01 16 01 00 02 03 0F 02 25 DD 7E
16:46:43
16:46:43
RX: 7E A0 2D 03 00 20 00 23 78 17 C6 16 03 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 01 00 8A 31 7E
16:46:43
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 5A 07 52 7E
16:46:44
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 5B 00 81 C8 02 04 12 00 2A 11 00 09 06 00 00 19 01 00 FF 02 02 01 0A 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 02 03 0F 0A 16 03 00 01 03 02 02 0F 01 16 00 02 02 0F 02 16 00 02 02 0F 03 16 00 02 04 12 00 2B 5B 0B 7E
16:46:44
16:46:44
RX: 7E A0 62 03 00 20 00 23 9C CF B9 11 00 09 06 00 00 19 02 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 2C 11 00 09 06 00 00 19 03 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 01 00 F2 DD 7E
16:46:44
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 5B 8E 43 7E
16:46:44
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 5C 00 81 E5 02 04 12 00 2D 11 00 09 06 00 00 19 04 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 2F 11 00 09 06 00 00 19 06 00 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 DD 3A 7E
16:46:44
16:46:44
RX: 7E A0 7F 03 00 20 00 23 B0 27 C9 16 01 00 02 03 0F 08 16 01 00 01 00 02 04 12 00 30 11 00 09 06 00 00 19 07 00 FF 02 02 01 0A 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 02 03 0F 0A 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 A3 69 7E
16:46:44
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 5C 31 37 7E
16:46:45
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 5D 00 81 AD 02 04 12 00 28 11 00 09 06 00 00 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 5A 11 01 09 06 00 00 1D 00 00 FF 02 02 01 0A 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 AD FF 7E
16:46:45
16:46:45
RX: 7E A0 47 03 00 20 00 23 D4 A3 E4 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 02 03 0F 0A 16 01 00 01 01 02 02 0F 01 16 01 48 2D 7E
16:46:45
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 5D B8 26 7E
16:46:45
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 5E 00 81 B5 02 04 12 00 5B 11 01 09 06 00 00 1D 01 00 FF 02 02 01 16 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 02 00 02 03 0F 06 16 01 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 02 03 0F 0A 16 03 00 02 03 0F 0B 16 01 00 02 03 0F 0C 16 03 00 02 03 0F 0D 16 03 00 02 03 0F 0E E9 5C 7E
16:46:45
16:46:45
RX: 7E A0 4F 03 00 20 00 23 F8 21 D1 16 03 00 02 03 0F 0F 16 03 00 02 03 0F 10 16 03 00 02 03 0F 11 16 03 00 02 03 0F 12 16 01 00 02 03 0F 13 16 01 00 02 03 0F 14 16 03 00 02 03 0F 15 16 03 00 02 03 0F 16 16 03 00 01 01 02 02 0F 01 16 01 D5 19 7E
16:46:45
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 5E 23 14 7E
16:46:46
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 5F 00 81 9A 02 04 12 00 5C 11 01 09 06 00 00 1D 02 00 FF 02 02 01 13 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 01 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 02 03 0F 0A 16 01 00 02 03 0F 0B 16 01 00 02 03 0F 0C 16 01 00 02 03 0F 0D 16 03 00 02 03 0F 0E A8 31 7E
16:46:46
16:46:46
RX: 7E A0 34 03 00 20 00 23 1C C5 17 16 03 00 02 03 0F 0F 16 01 00 02 03 0F 10 16 03 00 02 03 0F 11 16 03 00 02 03 0F 12 16 03 00 02 03 0F 13 16 03 00 01 00 1B B0 7E
16:46:46
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 5F AA 05 7E
16:46:46
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 60 00 81 D8 02 04 12 00 0F 11 01 09 06 00 00 28 00 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 02 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 01 04 02 02 0F 01 16 01 02 02 0F 02 16 00 02 02 0F 03 16 00 02 02 0F 04 16 00 02 04 12 00 0F 11 01 DC 7E
16:46:46
16:46:46
RX: 7E A0 72 03 00 20 00 23 30 60 63 01 09 06 00 00 28 00 01 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 02 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 01 04 02 02 0F 01 16 01 02 02 0F 02 16 00 02 02 0F 03 16 00 02 02 0F 04 16 00 D8 07 7E
16:46:46
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 60 DE CC 7E
16:46:47
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 61 00 81 D9 02 04 12 00 0F 11 01 09 06 00 00 28 00 02 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 02 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 01 04 02 02 0F 01 16 00 02 02 0F 02 16 00 02 02 0F 03 16 00 02 02 0F 04 16 00 02 04 12 00 11 11 AF 63 7E
16:46:47
16:46:47
RX: 7E A0 73 03 00 20 00 23 54 97 D9 00 09 06 00 00 29 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 00 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 10 06 7E
16:46:47
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 61 57 DD 7E
16:46:47
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 62 00 81 CE 02 04 12 00 40 11 00 09 06 00 00 2B 00 01 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 02 04 12 00 40 11 00 09 06 00 00 2B 00 02 FF 02 02 01 05 02 03 0F 01 16 01 00 02 03 0F 02 16 00 00 02 03 0F 03 16 00 00 02 03 0F 04 16 00 52 62 7E
16:46:47
16:46:48
RX: 7E A0 68 03 00 20 00 23 78 B2 F1 00 02 03 0F 05 16 00 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 01 11 00 09 06 00 00 2B 01 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 2B 01 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 24 3E 7E
16:46:48
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 62 CC EF 7E
16:46:48
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 63 00 81 D6 02 04 12 00 01 11 00 09 06 00 00 2B 01 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 46 11 00 09 06 00 00 60 03 0A FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 50 60 7E
16:46:48
16:46:48
RX: 7E A0 70 03 00 20 00 23 9C BD 3B 16 03 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 02 04 12 00 03 11 00 09 06 00 00 60 06 03 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 01 11 00 09 06 00 00 60 07 09 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 79 64 7E
16:46:48
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 63 45 FE 7E
16:46:48
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 64 00 81 C9 02 04 12 00 03 11 00 09 06 00 00 60 07 13 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 00 00 60 07 14 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 01 11 00 09 06 00 00 60 07 15 FF 02 02 01 CA 85 7E
16:46:48
16:46:49
RX: 7E A0 63 03 00 20 00 23 B0 74 CD 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 58 5F 7E
16:46:49
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 64 FA 8A 7E
16:46:49
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 65 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 0B 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 04 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 81 B2 7E
16:46:49
16:46:49
RX: 7E A0 6C 03 00 20 00 23 D4 A2 F1 00 00 60 0B 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0D 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0D 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 58 B4 7E
16:46:49
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 65 73 9B 7E
16:46:50
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 66 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 0E 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 83 DF 7E
16:46:50
16:46:50
RX: 7E A0 6C 03 00 20 00 23 F8 CC 1A 00 00 60 0F 16 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 2F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 3E FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 95 39 7E
16:46:50
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 66 E8 A9 7E
16:46:50
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 67 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 0F 3F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 5A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0F 5E FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 4E A8 7E
16:46:50
16:46:50
RX: 7E A0 6C 03 00 20 00 23 1C E6 BB 00 00 60 14 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 14 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 14 0A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 95 04 7E
16:46:50
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 67 61 B8 7E
16:46:51
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 68 00 81 DF 02 04 12 00 01 11 00 09 06 00 00 60 14 0F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 32 14 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 9D A7 7E
16:46:51
16:46:51
RX: 7E A0 79 03 00 20 00 23 30 E2 15 0F 01 16 00 02 04 12 00 01 11 00 09 06 00 00 60 32 1F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 32 2F FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 35 07 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 5D EC 7E
16:46:51
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 68 96 40 7E
16:46:51
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 69 00 81 D2 02 04 12 00 01 11 00 09 06 00 00 60 35 20 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 35 24 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 35 32 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 B5 8C 7E
16:46:51
16:46:51
RX: 7E A0 6C 03 00 20 00 23 54 AA 75 00 00 61 61 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 09 61 7E
16:46:51
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 69 1F 51 7E
16:46:52
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 6A 00 81 AF 02 04 12 00 01 11 00 09 06 00 00 61 62 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 0A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 0B FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 68 F1 7E
16:46:52
16:46:52
RX: 7E A0 49 03 00 20 00 23 78 E4 0D 00 00 61 62 14 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 15 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 AD D3 7E
16:46:52
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 6A 84 63 7E
16:46:52
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 6B 00 81 B2 02 04 12 00 07 11 01 09 06 00 00 63 62 00 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 07 11 01 09 06 00 00 63 62 01 FF 02 02 01 08 02 03 0F 01 16 01 5B BC 7E
16:46:52
16:46:52
RX: 7E A0 4C 03 00 20 00 23 9C 6D 5C 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 12 99 7E
16:46:52
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 6B 0D 72 7E
16:46:53
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 6C 00 81 B2 02 04 12 00 07 11 01 09 06 00 00 63 62 02 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 07 11 01 09 06 00 00 63 62 03 FF 02 02 01 08 02 03 0F 01 16 01 C7 93 7E
16:46:53
16:46:53
RX: 7E A0 4C 03 00 20 00 23 B0 03 B7 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 12 99 7E
16:46:53
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 6C B2 06 7E
16:46:53
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 6D 00 81 E3 02 04 12 00 07 11 01 09 06 00 00 63 62 04 FF 02 02 01 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 07 11 01 09 06 00 00 63 62 05 FF 02 02 01 08 02 03 0F 01 16 01 D9 CA 7E
16:46:53
16:46:54
RX: 7E A0 7D 03 00 20 00 23 D4 BE DB 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 16 11 00 09 06 00 01 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 B3 86 7E
16:46:54
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 6D 3B 17 7E
16:46:54
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 6E 00 81 DD 02 04 12 00 17 11 01 09 06 00 01 16 00 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 02 03 0F 08 16 03 00 02 03 0F 09 16 03 00 01 00 02 04 12 00 28 11 00 09 06 00 01 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 D1 48 7E
16:46:54
16:46:54
RX: 7E A0 77 03 00 20 00 23 F8 87 D9 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 46 11 00 09 06 00 01 60 03 0A FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 13 4F 7E
16:46:54
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 6E A0 25 7E
16:46:54
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 6F 00 81 BA 02 04 12 00 16 11 00 09 06 00 02 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 28 11 00 09 06 00 02 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 C8 53 7E
16:46:54
16:46:55
RX: 7E A0 54 03 00 20 00 23 1C 40 B3 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 46 11 00 09 06 00 02 60 03 0A FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 01 7C 7E
16:46:55
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 6F 29 34 7E
16:46:55
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 70 00 81 AE 02 04 12 00 16 11 00 09 06 00 03 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 28 11 00 09 06 00 03 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 23 D9 7E
16:46:55
16:46:55
RX: 7E A0 48 03 00 20 00 23 30 7D 5C 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 16 11 00 09 06 00 04 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 03 00 01 00 62 A1 7E
16:46:55
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 70 5F DC 7E
16:46:55
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 71 00 81 C9 02 04 12 00 28 11 00 09 06 00 04 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 16 11 00 09 06 00 05 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 E0 31 7E
16:46:55
16:46:56
RX: 7E A0 63 03 00 20 00 23 54 5E 6C 01 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 28 11 00 09 06 00 06 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 01 01 02 02 0F 01 16 01 78 AA 7E
16:46:56
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 71 D6 CD 7E
16:46:56
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 72 00 81 D8 02 04 12 00 28 11 00 09 06 00 07 19 09 00 FF 02 02 01 07 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 02 03 0F 05 16 03 00 02 03 0F 06 16 03 00 02 03 0F 07 16 03 00 01 01 02 02 0F 01 16 01 02 04 12 00 01 11 00 09 06 00 41 00 00 08 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 FE 46 7E
16:46:56
16:46:56
RX: 7E A0 72 03 00 20 00 23 78 2C AD 00 01 11 00 09 06 00 41 00 00 09 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 09 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 09 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 3F 38 7E
16:46:56
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 72 4D FF 7E
16:46:56
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 73 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 00 09 0B FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 01 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 01 18 00 FF 02 02 01 20 E0 7E
16:46:56
16:46:57
RX: 7E A0 5A 03 00 20 00 23 9C 69 B1 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 72 3D 7E
16:46:57
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 73 C4 EE 7E
16:46:57
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 74 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 02 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 03 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 04 07 00 FF 02 02 01 47 CE 7E
16:46:57
16:46:57
RX: 7E A0 5A 03 00 20 00 23 B0 07 5A 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 05 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 A2 AC 7E
16:46:57
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 74 7B 9A 7E
16:46:58
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 75 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 06 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 07 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 08 07 00 FF 02 02 01 3D 38 7E
16:46:58
16:46:58
RX: 7E A0 5A 03 00 20 00 23 D4 25 7F 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 09 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 51 AF 7E
16:46:58
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 75 F2 8B 7E
16:46:58
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 76 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 0A 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0C 1F 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0C 23 00 FF 02 02 01 B3 CA 7E
16:46:58
16:46:58
RX: 7E A0 5A 03 00 20 00 23 F8 4B 94 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0C 27 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 10 10 7E
16:46:58
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 76 69 B9 7E
16:46:59
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 77 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 0C 2B 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0C 2C 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0C 2D 00 FF 02 02 01 9E 84 7E
16:46:59
16:46:59
RX: 7E A0 5A 03 00 20 00 23 1C 61 35 03 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0D 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 F4 AA 7E
16:46:59
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 77 E0 A8 7E
16:46:59
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 78 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 0E 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 0F 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 0F 18 00 FF 02 02 01 C1 0A 7E
16:46:59
16:46:59
RX: 7E A0 5A 03 00 20 00 23 30 0F DE 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 72 3D 7E
16:46:59
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 78 17 50 7E
16:47:00
RX: 7E A8 8C 03 00 20 00 23 52 B8 1F E6 E7 00 C4 02 C1 00 00 00 00 79 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 10 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 05 11 00 09 06 01 00 10 18 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 E3 AC 7E
16:47:00
16:47:00
RX: 7E A0 5A 03 00 20 00 23 54 2D FB 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 02 04 12 00 03 11 00 09 06 01 00 15 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 DA 7C 7E
16:47:00
TX: 7E A0 16 00 20 00 23 03 74 60 80 E6 E6 00 C0 02 C1 00 00 00 79 9E 41 7E
16:47:00
RX: 7E A8 8C 03 00 20 00 23 76 9E 78 E6 E7 00 C4 02 C1 00 00 00 00 7A 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 16 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 17 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 18 07 00 FF 02 02 01 5C 0B 7E
16:47:00
16:47:01
RX: 7E A0 5A 03 00 20 00 23 78 43 10 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 19 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 1A 52 7E
16:47:01
TX: 7E A0 16 00 20 00 23 03 B6 7E 65 E6 E6 00 C0 02 C1 00 00 00 7A 05 73 7E
16:47:01
RX: 7E A8 8C 03 00 20 00 23 9A FC 55 E6 E7 00 C4 02 C1 00 00 00 00 7B 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 1A 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 1B 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 1C 07 00 FF 02 02 01 26 65 7E
16:47:01
16:47:01
RX: 7E A0 5A 03 00 20 00 23 9C 69 B1 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 1D 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 44 AB 7E
16:47:01
TX: 7E A0 16 00 20 00 23 03 F8 04 CE E6 E6 00 C0 02 C1 00 00 00 7B 8C 62 7E
16:47:01
RX: 7E A8 8C 03 00 20 00 23 BE DA 32 E6 E7 00 C4 02 C1 00 00 00 00 7C 00 81 C1 02 04 12 00 03 11 00 09 06 01 00 1E 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 15 11 00 09 06 01 00 1F 04 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 03 00 02 03 0F 03 16 03 00 02 03 0F 04 16 03 00 01 00 02 04 12 00 05 11 00 09 06 01 00 1F 04 00 FF 02 02 97 5D 7E
16:47:01
16:47:02
RX: 7E A0 5B 03 00 20 00 23 B0 D2 C5 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 03 00 01 02 02 02 0F 01 16 00 02 02 0F 02 16 00 6B 34 7E
16:47:02
TX: 7E A0 16 00 20 00 23 03 3A 1A 2B E6 E6 00 C0 02 C1 00 00 00 7C 33 16 7E
16:47:02
RX: 7E A8 8C 03 00 20 00 23 D2 B0 9B E6 E7 00 C4 02 C1 00 00 00 00 7D 00 81 E3 02 04 12 00 03 11 00 09 06 01 00 1F 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 20 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 20 18 00 FF 02 02 01 4C 1C 7E
16:47:02
16:47:02
RX: 7E A0 7D 03 00 20 00 23 D4 BE DB 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 01 11 00 09 06 01 00 20 20 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 20 21 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 0A 8E 7E
16:47:02
TX: 7E A0 16 00 20 00 23 03 7C 28 0C E6 E6 00 C0 02 C1 00 00 00 7D BA 07 7E
16:47:02
RX: 7E A8 8C 03 00 20 00 23 F6 96 FC E6 E7 00 C4 02 C1 00 00 00 00 7E 00 81 D6 02 04 12 00 03 11 00 09 06 01 00 20 22 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 01 11 00 09 06 01 00 20 24 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 20 25 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 96 C6 7E
16:47:02
16:47:03
RX: 7E A0 70 03 00 20 00 23 F8 9F 1E 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 20 26 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 01 11 00 09 06 01 00 20 28 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 A8 ED 7E
16:47:03
TX: 7E A0 16 00 20 00 23 03 BE 36 E9 E6 E6 00 C0 02 C1 00 00 00 7E 21 35 7E
16:47:03
RX: 7E A8 8C 03 00 20 00 23 1A F4 D1 E6 E7 00 C4 02 C1 00 00 00 00 7F 00 81 C0 02 04 12 00 03 11 00 09 06 01 00 21 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 23 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 51 07 28 FF 02 02 01 42 30 7E
16:47:03
16:47:03
RX: 7E A0 5A 03 00 20 00 23 1C 61 35 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 54 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 A9 06 7E
16:47:03
TX: 7E A0 16 00 20 00 23 03 F0 4C 42 E6 E6 00 C0 02 C1 00 00 00 7F A8 24 7E
16:47:04
RX: 7E A8 8C 03 00 20 00 23 3E D2 B6 E6 E7 00 C4 02 C1 00 00 00 00 80 00 81 DC 02 04 12 00 03 11 00 09 06 01 00 55 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 03 11 00 09 06 01 00 5A 07 00 FF 02 02 01 03 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 01 01 02 02 0F 01 16 00 02 04 12 00 07 11 01 09 06 01 00 63 61 00 FF 02 02 01 35 16 7E
16:47:04
16:47:04
RX: 7E A0 76 03 00 20 00 23 30 16 0C 08 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 00 02 04 12 00 01 11 00 09 06 01 03 00 02 08 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 11 50 7E
16:47:04
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 80 D0 2B 7E
16:47:04
RX: 7E A0 2E 03 00 20 00 23 52 21 E0 E6 E7 00 C4 02 C1 01 00 00 00 81 00 15 02 04 12 00 00 11 00 09 06 E8 37 00 20 00 00 02 02 01 00 01 00 92 CE 7E
16:47:04
TX: 7E A0 77 00 20 00 23 03 54 32 9A E6 E6 00 C0 03 C1 0A 00 03 01 00 00 06 00 FF 03 00 00 03 01 00 00 06 01 FF 03 00 00 03 01 00 00 06 02 FF 03 00 00 03 01 00 00 06 03 FF 03 00 00 04 01 00 01 02 00 FF 03 00 00 04 01 00 01 02 01 FF 03 00 00 04 01 00 01 02 02 FF 03 00 00 04 01 00 01 02 03 FF 03 00 00 04 01 00 01 02 04 FF 03 00 00 05 01 00 01 04 00 FF 04 00 73 9D 7E
16:47:05
RX: 7E A0 21 03 00 20 00 23 74 E1 BD E6 E7 00 C4 02 C1 00 00 00 00 01 00 08 0A 00 02 02 0F FF
16 23 C7 AE 7E
16:47:05
TX: 7E A0 16 00 20 00 23 03 BA 12 AF E6 E6 00 C0 02 C1 00 00 00 01 51 BE 7E
16:47:05
RX: 7E A0 0A 03 00 20 00 23 71 4D FF 7E
16:47:05
TX: 7E A0 16 00 20 00 23 03 DC 22 A9 E6 E6 00 C0 02 C1 00 00 00 02 CA 8C 7E
16:47:05
16:47:05
TX: 7E A0 16 00 20 00 23 03 FE 32 AB E6 E6 00 C0 02 C1 00 00 00 03 43 9D 7E
16:47:05
16:47:05
TX: 7E A0 16 00 20 00 23 03 10 42 A5 E6 E6 00 C0 02 C1 00 00 00 04 FC E9 7E
16:47:05
16:47:05
TX: 7E A0 16 00 20 00 23 03 32 52 A7 E6 E6 00 C0 02 C1 00 00 00 05 75 F8 7E
16:47:05
16:47:05
TX: 7E A0 16 00 20 00 23 03 54 62 A1 E6 E6 00 C0 02 C1 00 00 00 06 EE CA 7E
16:47:06
16:47:06
TX: 7E A0 16 00 20 00 23 03 76 72 A3 E6 E6 00 C0 02 C1 00 00 00 07 67 DB 7E
16:47:11 Data send failed. Try to resend 1/3 7E A0 1A 03 00 20 00 23 96 35 D9 E6 E7 00 C4 02 C1 02 00 00 00 02 01 0F 00 9B 14 7E
16:47:11
RX: 7E A0 1A 03 00 20 00 23 96 35 D9 E6 E7 00 C4 02 C1 02 00 00 00 02 01 0F 00 9B 14 7E 7E A0 0A 03 00 20 00 23 91 43 18 7E
16:47:11
TX: 7E A0 16 00 20 00 23 03 98 02 AD E6 E6 00 C0 02 C1 00 00 00 08 90 23 7E
16:47:16 Data send failed. Try to resend 1/3 7E A0 1A 03 00 20 00 23 B8 49 11 E6 E7 00 C4 02 C1 02 00 00 00 03 01 0F 00 20 08 7E
16:47:16
RX: 7E A0 1A 03 00 20 00 23 B8 49 11 E6 E7 00 C4 02 C1 02 00 00 00 03 01 0F 00 20 08 7E 7E A0 0A 03 00 20 00 23 B1 41 39 7E
16:47:16
TX: 7E A0 16 00 20 00 23 03 BA 12 AF E6 E6 00 C0 02 C1 00 00 00 09 19 32 7E
Thanks!
Laura Chu
4 years 10 months ago
Issues appears at the end of the log.
Your meter can't handle GetRequestWithList and it returns invalid data. Inform meter manufacturer of this. You can fix this on the client-side if you don't use the multiple references service.
Select meter settings and select "Supported Services" tab. Remove "Multiple references" and connect again.
https://www.gurux.fi/Gurux.DLMS.Conformance#MultipleReferences
Laura Chu
Got it! Thank you very much~!
  • amir.jradi
  • JOEBID€N123
  • yogibear
  • Eric@li