Meter Connect Success but Register Reading Fail

Forum Rules

Before commenting read Forum rules

Don't comment the topic if you have a new question.

You can create a new topic selecting correct category from Gurux Forum and then create a new topic selecting "New Topic" from the top left.

By abu3bdullah , 22 October, 2020
Forums
DLMSDirector

I am connecting to the Meter using "Serial over Ethernet", the connection is successfully done.

When I try to read for example the "1.0.1.8.0.255" register, DLMSDirector is sending and receiving without any problems, but I don't have any values.

When I repeat the "Read" process about three times, I receive "" then connect again to meter and "Read" again it I receive correct value !

14:45:09 Read object type Register index: 2
TX: 7E A0 1C 00 02 66 0D 07 32 22 9E E6 E6 00 C0 01 C1 00 03 01 00 01 08 00 FF 02 00 32 68 7E

"No Value is got here"
14:45:10
RX:
7E A0 1C 00 02 66 0D 07 32 22 9E E6 E6 00 C0 01 C1 00 03 01 00 01 08 00 FF 02 00 32 68 7E
7E A0 2A 07 00 02 66 0D 03 65 00 E6 E7 00 C2 09 0C 07 E4 0A 16 04 0E 2D 10 00 80 00 00 00 01 00 00 61 61 04 FF 02 04 08 40 04 CE 7E

"Value is received"
14:48:33
RX:
7E A0 1C 00 02 66 0D 07 32 22 9E E6 E6 00 C0 01 C1 00 03 01 00 01 08 00 FF 02 00 32 68 7E
7E A0 1C 07 00 02 66 0D 52 EE CD E6 E7 00 C4 01 C1 00 15 00 00 00 00 00 2C BA F1 50 C0 7E

The problem is repetitive, and I tried for many meters and have the same behavior. But sometimes I receive the value from the first "Read".

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

You are receiving GatewayRequest and the HDLC frame is the supervisory frame. This is wrong and the client accepts it as a reply. Are you communicating directly with the meter or is there a gateway in the middle?

BR,
Mikko

abu3bdullah

5 years 7 months ago

Yes I am just using a "Serial

Yes I am just using a "Serial to Ethernet" Converter in the middle.

Meter:RS485 > Converter > IP:Port
The serial port of the converter is mapped to IP & Port, I am using "Serial over Ethernet" option in Gurux configuration.

It was working most of the time, but sometimes I have this behavior.

abu3bdullah

5 years 5 months ago

Still this issue I have with

Still this issue I have with Gurux.AMI
Please can you consider ?

The value is stored in the DB as Empty value ' '
And it is almost repeated for 1 meter of 176, sometimes the problem shows in other meters but less often.

Profile picture for user Kurumi

Kurumi

5 years 5 months ago

Hi,

Hi,

Your meter is sending EventNotificationReques where HDLC sequence ID is 3. We have improved this and the new version is released at the beginning of January.

BR,
Mikko

  • Create new account
  • Reset your password

Hire Us!

Latest Releases

  • Tue, 06/09/2026 - 11:16
    gurux.dlms.java 4.0.95
  • Tue, 06/09/2026 - 10:03
    Gurux.DLMS.Python 1.0.199
  • Mon, 06/08/2026 - 13:39
    gurux.dlms.cpp 9.0.2606.0801
  • Mon, 06/01/2026 - 10:15
    gurux.dlms.cpp 9.0.2606.0101
  • Thu, 05/28/2026 - 16:06
    gurux.dlms.java 4.0.94

New forum topics

  • Error reading L&G Meter
  • Pass a TCP Client to GXNet
  • Australian EDMI Mk10D (Essential Energy area)
  • Strange mix of data notificiation vs get response
  • DLMS Connection
More

Who's new

  • Tuanhgg
  • Adel
  • charnon
  • Paddles
  • Miguel Ángel
RSS feed
Privacy FAQ GXDN Issues Contact
Follow Gurux on Twitter Follow Gurux on Linkedin