By jediace , 1 April, 2019 Forums General discussion Hi! i have in pdf-manual Landys+gir this value: 2.8.0 Energia totale attiva A - 2.8.0.W Energia totale attiva mese precedente A - in register (GXDLMSDirector, serial connection) i have 1.1.2.8.0.255 = "Time integral 1, total, current billing period" so 2.8.0 = 1.1.2.8.0.255 ok.. but where i can find 2.8.0.W?? thx Hi, Hi, As you have find out, in IEC logical name is using 3 letters and in DLMS there are 6 dotted numbers. You can get this info from meter manual or meter vendor. BR, Mikko
Hi, Hi, As you have find out, in IEC logical name is using 3 letters and in DLMS there are 6 dotted numbers. You can get this info from meter manual or meter vendor. BR, Mikko
Hi,
Hi,
As you have find out, in IEC logical name is using 3 letters and in DLMS there are 6 dotted numbers.
You can get this info from meter manual or meter vendor.
BR,
Mikko