  3. AARE Validation Failed
AARE validation failed
By Bhaumik , 31 August, 2020
I am testing IS15959-2 meter.
Following is the AARQ and AARE payloads.
AARQ:
7ea0600341100c1ce6e6006052a109060760857405080103a60a04085a454e30303039338a0207808b0760857405080201ac07800568656c6c6fbe230421211f3000000099cdf77460be650708c7c49b63e11617e7aa955426ab0c9a1918e617437e
AARE:
7EA02D4103302E66E6E700611FA109060760857405080101A203020101A305A103020102BE0604040E01000439E47E
In AARE validation got "ServiceError Initiate Error exception. ApplicationReference ApplicationContextUnsupported" Error Message.
I have configured the same configuration for other meters having the same firmware version. It is working properly in another meter.
Can you please check and provide an update from the payload.
6 years 2 months ago
I believe that this meter is not supporting ciphering. Try to remove ciphering.
Bhaumik
After doing a power down up to a meter, Got proper AARE response with ciphering.
So, How it is possible? Can you please provide our inputs.
You need to ask this from the meter manufacturer. There is nothing that we can do for it.