By Bhavjinder Singh, 3 July, 2018 Forums DLMSDirector Below is the trace content coming in the GXDLMSDIRECTOR: 03/07/2018 10:55:45 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="53" /> <DisconnectRequest> </DisconnectRequest> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="43" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="10" /> <PDU> <AssociationRequest> <ApplicationContextName Value="LN" /> <SenderACSERequirements Value="1" /> <MechanismName Value="Low" /> <CallingAuthentication Value="4142434430303031" /> <InitiateRequest> <ProposedDlmsVersionNumber Value="06" /> <ProposedConformance> </ProposedConformance> <ProposedMaxPduSize Value="FFFF" /> </InitiateRequest> </AssociationRequest> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="2C" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="30" /> <PDU> <AssociationResponse> <ApplicationContextName Value="LN" /> <AssociationResult Value="01" /> <ResultSourceDiagnostic> <ACSEServiceUser Value="01" /> </ResultSourceDiagnostic> <ConfirmedServiceError> <Service Value="01" /> <ServiceError> <Initiate Value="IncompatibleConformance" /> </ServiceError> </ConfirmedServiceError> </AssociationResponse> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> NOt able to connect to meter It's an indian make meter... NOt able to connect to meter I have also tried with client address: 10 but no luck.. pls help me NOt able to connect to meter Hi Mikko.. pls help me.. Im trying to connect meter with GXDLMSDIRECTOR so that i can understand better understand communication.. Meter im reading is of indian make. but im getting following error in the trace: <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="53" /> <DisconnectRequest> </DisconnectRequest> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="43" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="10" /> <PDU> <AssociationRequest> <ApplicationContextName Value="LN" /> <SenderACSERequirements Value="1" /> <MechanismName Value="Low" /> <CallingAuthentication Value="4142434430303031" /> <InitiateRequest> <ProposedDlmsVersionNumber Value="06" /> <ProposedConformance> </ProposedConformance> <ProposedMaxPduSize Value="FFFF" /> </InitiateRequest> </AssociationRequest> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="2C" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="30" /> <PDU> <AssociationResponse> <ApplicationContextName Value="LN" /> <AssociationResult Value="01" /> <ResultSourceDiagnostic> <ACSEServiceUser Value="01" /> </ResultSourceDiagnostic> <ConfirmedServiceError> <Service Value="01" /> <ServiceError> <Initiate Value="IncompatibleConformance" /> </ServiceError> </ConfirmedServiceError> </AssociationResponse> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> Not able to connect to meter Hi, You have not selected any Conformance. You can see this selecting "Supported services" -tab from device settings. Select at least Get. BR, Mikko Log in or register to post comments
NOt able to connect to meter Hi Mikko.. pls help me.. Im trying to connect meter with GXDLMSDIRECTOR so that i can understand better understand communication.. Meter im reading is of indian make. but im getting following error in the trace: <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="53" /> <DisconnectRequest> </DisconnectRequest> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="9" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="93" /> <Snrm> </Snrm> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="43" > <TargetAddress Value="1" /> <SourceAddress Value="20" /> <FrameType Value="10" /> <PDU> <AssociationRequest> <ApplicationContextName Value="LN" /> <SenderACSERequirements Value="1" /> <MechanismName Value="Low" /> <CallingAuthentication Value="4142434430303031" /> <InitiateRequest> <ProposedDlmsVersionNumber Value="06" /> <ProposedConformance> </ProposedConformance> <ProposedMaxPduSize Value="FFFF" /> </InitiateRequest> </AssociationRequest> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="2C" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="30" /> <PDU> <AssociationResponse> <ApplicationContextName Value="LN" /> <AssociationResult Value="01" /> <ResultSourceDiagnostic> <ACSEServiceUser Value="01" /> </ResultSourceDiagnostic> <ConfirmedServiceError> <Service Value="01" /> <ServiceError> <Initiate Value="IncompatibleConformance" /> </ServiceError> </ConfirmedServiceError> </AssociationResponse> </PDU> </HDLC> 03/07/2018 10:55:59 AM <HDLC len="1E" > <TargetAddress Value="20" /> <SourceAddress Value="1" /> <FrameType Value="73" /> <PDU> <Ua> <MaxInfoTX Value="256" /> <MaxInfoRX Value="128" /> <WindowSizeTX Value="1" /> <WindowSizeRX Value="1" /> </Ua> </PDU> </HDLC>
Not able to connect to meter Hi, You have not selected any Conformance. You can see this selecting "Supported services" -tab from device settings. Select at least Get. BR, Mikko
NOt able to connect to meter
It's an indian make meter...
NOt able to connect to meter
I have also tried with client address: 10 but no luck.. pls help me
NOt able to connect to meter
Hi Mikko.. pls help me..
Im trying to connect meter with GXDLMSDIRECTOR so that i can understand better understand communication.. Meter im reading is of indian make.
but im getting following error in the trace:
<HDLC len="9" >
<TargetAddress Value="1" />
<SourceAddress Value="20" />
<FrameType Value="93" />
<Snrm>
</Snrm>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="9" >
<TargetAddress Value="1" />
<SourceAddress Value="20" />
<FrameType Value="53" />
<DisconnectRequest>
</DisconnectRequest>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="1E" >
<TargetAddress Value="20" />
<SourceAddress Value="1" />
<FrameType Value="73" />
<PDU>
<Ua>
<MaxInfoTX Value="256" />
<MaxInfoRX Value="128" />
<WindowSizeTX Value="1" />
<WindowSizeRX Value="1" />
</Ua>
</PDU>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="9" >
<TargetAddress Value="1" />
<SourceAddress Value="20" />
<FrameType Value="93" />
<Snrm>
</Snrm>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="1E" >
<TargetAddress Value="20" />
<SourceAddress Value="1" />
<FrameType Value="73" />
<PDU>
<Ua>
<MaxInfoTX Value="256" />
<MaxInfoRX Value="128" />
<WindowSizeTX Value="1" />
<WindowSizeRX Value="1" />
</Ua>
</PDU>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="43" >
<TargetAddress Value="1" />
<SourceAddress Value="20" />
<FrameType Value="10" />
<PDU>
<AssociationRequest>
<ApplicationContextName Value="LN" />
<SenderACSERequirements Value="1" />
<MechanismName Value="Low" />
<CallingAuthentication Value="4142434430303031" />
<InitiateRequest>
<ProposedDlmsVersionNumber Value="06" />
<ProposedConformance>
</ProposedConformance>
<ProposedMaxPduSize Value="FFFF" />
</InitiateRequest>
</AssociationRequest>
</PDU>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="2C" >
<TargetAddress Value="20" />
<SourceAddress Value="1" />
<FrameType Value="30" />
<PDU>
<AssociationResponse>
<ApplicationContextName Value="LN" />
<AssociationResult Value="01" />
<ResultSourceDiagnostic>
<ACSEServiceUser Value="01" />
</ResultSourceDiagnostic>
<ConfirmedServiceError>
<Service Value="01" />
<ServiceError>
<Initiate Value="IncompatibleConformance" />
</ServiceError>
</ConfirmedServiceError>
</AssociationResponse>
</PDU>
</HDLC>
03/07/2018 10:55:59 AM
<HDLC len="1E" >
<TargetAddress Value="20" />
<SourceAddress Value="1" />
<FrameType Value="73" />
<PDU>
<Ua>
<MaxInfoTX Value="256" />
<MaxInfoRX Value="128" />
<WindowSizeTX Value="1" />
<WindowSizeRX Value="1" />
</Ua>
</PDU>
</HDLC>
Not able to connect to meter
Hi,
You have not selected any Conformance. You can see this selecting "Supported services" -tab from device settings.
Select at least Get.
BR,
Mikko