I am trying to communicate with Actaris ACE5000 meter. The parameters selected are:
Client address : 10
Physical Server : 11
Logical Server : 1
Wait time : 5
Authentication : None
Media : Serial
Manufacturer : Actaris Electricity
Start Protocol : DLMS.
Logical Name Refrencing : true.
When I try to connect, I get a response "Failed to recieve reply from device in given time". How can I fix it?
Thanks and Best regards
Your meter is supporting IEC 61107. IEC start protocol means that IEC is used to move Mode E and then start to use DLMS. GXDLMSDirector doesn't support IEC 61107. Is there DLMS label on the cover on the meter?
Hi,
Hi,
Are you using an optical probe (head) or serial port connection? What is your meter version?
BR,
Mikko
Dear Mikko, I can read the
Dear Mikko, I can read the meter using IEC 61107 optical port. I tried DLMSDirector with IEC Start Protocol but I couldn't. Best regards
Hi,
Hi,
Your meter is supporting IEC 61107. IEC start protocol means that IEC is used to move Mode E and then start to use DLMS. GXDLMSDirector doesn't support IEC 61107. Is there DLMS label on the cover on the meter?
BR,
Mikko