  2. Writing TOU Profile Configurations: Error "Service Not Allowed"
writing TOU profile configurations: Error "Service not allowed"
By intellismartinfra , 19 December, 2025
We are writing TOU profile configurations, and it is getting success if payload size is less than 512 Byte, but if size of the payload is greater than 512 bytes so getting error that "Service not allowed".
Meter negotiated hdlc TX/RX = 128 Byte and MaxPdu Size 512 Byte
Below are the Two Payload, with one which is < 512 is getting Success:
1- Write Success:
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
2- Write Fail: with 2nd which is > 512 is getting Fail:
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
Exception Error:
{Gurux.DLMS.GXDLMSExceptionResponse: Exception response. "Service not allowed"-exception. Operation not possible
at Gurux.DLMS.GXDLMS.HandleExceptionResponse(GXReplyData data) in \\Gurux.DLMS.Development\GXDLMS.cs:line 5407
at Gurux.DLMS.GXDLMS.GetPdu(GXDLMSSettings settings, GXReplyData data) in \\Gurux.DLMS.Development\GXDLMS.cs:line 5725
at Gurux.DLMS.GXDLMS.GetData(GXDLMSSettings settings, GXByteBuffer reply, GXReplyData data, GXReplyData notify) in \\Gurux.DLMS.Development\GXDLMS.cs:line 6404
at Gurux.DLMS.GXDLMSClient.GetData(GXByteBuffer reply, GXReplyData data, GXReplyData notify) in \\Gurux.DLMS.Development\GXDLMSClient.cs:line 3123
at \\.HHU.App.Helper.DeviceAssociation.ReadDLMSPacket(Byte[] data, GXReplyData reply) in \\\\.HHU.App\Helper\DeviceAssociation.cs:line 692
at \\.HHU.App.Helper.DeviceAssociation.ReadDataBlock(Byte[] data, GXReplyData reply) in \\\\.HHU.App\Helper\DeviceAssociation.cs:line 565
at \\.HHU.App.Helper.DeviceAssociation.ReadDataBlock(Byte[][] data, GXReplyData reply) in \\\\.HHU.App\Helper\DeviceAssociation.cs:line 558
at \\.HHU.App.ViewModel.TOUViewModel.TOUPassiveDayProfileRead() in \\\\.HHU.App\ViewModel\TOUViewModel.cs:line 70}
intellismartinfra
5 months 2 weeks ago
@GuruX expert team: can you…
@GuruX expert team: can you please help regarding this issue...no input as of now how to procced on it.
Hi, You need to give the…
You need to give the complete communication log. Now the HDLC frames are missing, and I can't verify this without the log.
intellismartinfra
Thanks for your comments…
Thanks for your comments.
below are the complete log in both Scenario Success & Fail with same meter, only change in payload (reduction in data successfully write with GuruXDirector)
Fail: Error "Service not allowed"
14:47:59 Send SNRM request.
14:47:59
14:47:59 Send AARQ request.
14:47:59
RX: 7E A0 37 21 03 30 6C 7C E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 00 10 02 00 00 07 1C EA 7E
14:47:59
RX: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 00 22 6D 1A 7E
14:47:59 Disconnect request
14:48:00
14:48:00 Send SNRM request.
TX: 7E A0 07 03 61 93 69 47 7E
14:48:00
RX: 7E A0 1E 61 03 73 B5 7C 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
14:48:00 Send AARQ request.
TX: 7E A0 6B 03 61 10 2A FF E6 E6 00 60 5D A1 09 06 07 60 85 74 05 08 01 03 A6 0A 04 08 49 4E 54 45 53 4D 30 36 8A 02 07 80 8B 07 60 85 74 05 08 02 02 AC 12 80 10 1F 10 63 6C 04 25 04 66 77 0C 11 5D 67 12 63 23 BE 23 04 21 21 1F 30 00 00 00 23 49 90 0D E7 08 DE 38 55 5C 27 E9 D2 BC 2D 18 E5 16 4E F4 7E 02 F3 DF 1A FE 4A 33 FA 7E
14:48:00
RX: 7E A0 77 61 03 30 AD 6C E6 E7 00 61 69 A1 09 06 07 60 85 74 05 08 01 03 A2 03 02 01 00 A3 05 A1 03 02 01 0E A4 0A 04 08 49 4E 54 00 00 00 00 00 88 02 07 80 89 07 60 85 74 05 08 02 02 AA 12 80 10 61 62 63 64 65 66 67 68 69 6A 6B 6C 6D 6E 6F 70 BE 23 04 21 28 1F 30 00 00 00 22 A4 C0 67 FA E3 B1 6E 13 E4 4F 6C DF A9 6D 28 A9 13 A2 0C 74 49 CA 60 74 37 27 66 9F 7E
14:48:00 Authenticating.
TX: 7E A0 3E 03 61 32 7B 46 E6 E6 00 CB 30 30 00 00 00 24 45 14 5A 2E A0 34 E4 9A 52 CE C1 CC C0 C3 A9 E2 4E E6 EF 09 CD 41 FE 4C FA 74 75 86 16 98 18 91 55 62 8B B4 B4 C2 46 40 B8 00 33 D3 AB 7E
14:48:00
RX: 7E A0 37 61 03 52 0E 3A E6 E7 00 CF 29 30 00 00 00 23 1D E9 E8 C4 19 C8 25 7F 83 CD 53 2E 02 DC 8B 02 D1 70 8F 02 99 D4 A9 B7 92 0A 64 E0 55 2E A1 A6 33 1E FF C0 97 DD 7E
14:48:14 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A8 89 03 61 54 D6 2C E6 E6 00 E0 01 00 01 00 00 82 01 F9 C9 82 02 98 30 00 00 00 25 16 12 CD 09 A0 BD D4 D9 97 CF FF 20 20 CB 9D 42 74 9C FB 5F A8 06 60 F0 5A B9 20 69 2A 0A 50 7F 0B 0B AC 6D 38 CB AF 51 FC 1B 21 9C E0 8B A9 BE 0F C4 DB 4E 22 DB 47 65 69 DB 7D 95 2D CD F7 E1 1F 3C B1 B6 05 DC ED 9E F4 AF 0F 10 A6 71 44 6E 2C 90 65 A5 22 88 28 65 88 A2 61 FA 44 63 8D 0C 7A 4E 56 80 CD 82 ED B4 D3 31 6A 55 3A 7E
14:48:14
RX: 7E A0 07 61 03 71 65 65 7E
TX: 7E A8 89 03 61 56 C4 0F B2 C3 4C 40 B2 9F F9 68 E0 2A 40 92 FF BD 07 13 DC 21 AC 7D 99 49 EA AE 6C C2 47 68 8C 06 46 69 93 11 9E C5 07 82 67 81 B0 14 5B 4E 78 3C 32 05 E6 B6 BA 2D 4D 4A BE 01 D6 F9 33 53 CF 5F 6C 2E C0 FC 3F 61 75 24 81 A1 67 FC 27 20 13 5A 6D 88 27 99 53 F8 B7 A7 BF 60 9D 67 31 C3 0F E3 55 6D AD 4F D7 C3 2C 64 84 74 C1 AF BE 9F A5 75 9E DC 7D 50 3D 4C 6A 35 41 90 EB 8F BD 0E 2E 0D DD DC 45 54 7E
14:48:14
RX: 7E A0 07 61 03 91 6B 82 7E
TX: 7E A8 89 03 61 58 BA E6 31 61 19 B0 29 F0 70 A6 87 73 01 64 4A 92 0D 28 22 79 67 C5 AF 66 C5 3D 43 D1 E7 7D 7F E1 99 86 48 93 0F 44 46 6E DC 29 17 4B 29 1D 79 35 25 C8 F9 3D A9 33 91 2F C0 89 19 EB BE BE D9 0C E3 51 BC EC 66 DB 46 88 04 49 28 81 CA 68 A3 F6 91 80 7C DF 70 B1 C9 3D A9 E9 4F D7 0D 53 B9 C9 58 40 DD 2B 07 50 DE C6 96 72 82 30 B4 41 58 5F 6B D6 D4 1D CD FA 2D 77 7A B1 1E 71 03 A0 07 98 24 9B E7 75 7E
14:48:14
RX: 7E A0 07 61 03 B1 69 A3 7E
TX: 7E A8 89 03 61 5A A8 C5 32 8D 13 85 46 5C 1C 30 07 C9 50 EC 12 D1 46 98 58 58 9D CB 4D 18 DB CB ED 6B 16 1F 79 BA 03 9A 6C F0 7C DC D7 4C FA 44 3D 84 88 D6 1E 8A F6 A5 6C B7 D2 F6 0F 64 70 5A 25 7F EF CD D3 70 5B 1E BE BE 65 AB 27 8F A6 AC A6 42 6F CD C6 4E DC 81 B3 30 67 46 81 CF E0 00 8D 88 FD 5F 09 D8 16 7C 1D 77 82 F8 83 19 1D 70 BE 4B 71 C0 3E 3C 38 1B 60 B6 FD F8 AB ED EB DA 92 0C 00 98 2F C6 B3 5F 1C 64 7E
14:48:14
RX: 7E A0 07 61 03 D1 6F C0 7E
TX: 7E A0 0E 03 61 5C F1 80 E0 53 FC 27 B4 4E E3 7E
14:48:14
RX: 7E A0 0F 61 03 F4 18 53 E6 E7 00 D8 01 01 3C 43 7E
Pass: Successful Write
14:56:37 Send SNRM request.
14:56:37
14:56:37 Send AARQ request.
14:56:37
14:56:37
RX: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 00 48 31 D6 7E
14:56:37 Disconnect request
14:56:38
14:56:38 Send SNRM request.
14:56:38
14:56:38 Send AARQ request.
TX: 7E A0 6B 03 61 10 2A FF E6 E6 00 60 5D A1 09 06 07 60 85 74 05 08 01 03 A6 0A 04 08 49 4E 54 45 53 4D 30 36 8A 02 07 80 8B 07 60 85 74 05 08 02 02 AC 12 80 10 45 77 48 27 4F 2D 31 2B 1C 14 43 67 3D 2E 1D 0D BE 23 04 21 21 1F 30 00 00 00 49 7F 52 C7 95 97 BA 01 6D D3 26 CA C3 2B 65 C1 D3 65 DE F7 AB 3E 66 6E 92 AE 2B 74 2F 7E
14:56:38
RX: 7E A0 77 61 03 30 AD 6C E6 E7 00 61 69 A1 09 06 07 60 85 74 05 08 01 03 A2 03 02 01 00 A3 05 A1 03 02 01 0E A4 0A 04 08 49 4E 54 00 00 00 00 00 88 02 07 80 89 07 60 85 74 05 08 02 02 AA 12 80 10 61 62 63 64 65 66 67 68 69 6A 6B 6C 6D 6E 6F 70 BE 23 04 21 28 1F 30 00 00 00 45 8D E7 FC B1 11 43 08 B4 78 4F AF 4B EC 06 BC C4 7F 37 6A D6 7A C7 55 21 4E 51 18 76 7E
14:56:38 Authenticating.
TX: 7E A0 3E 03 61 32 7B 46 E6 E6 00 CB 30 30 00 00 00 4A 8C 1E D5 EC 87 A9 AD 98 C4 F4 D0 02 A0 F0 3E 33 C8 33 AD 80 51 A4 CC 4F EB CC 5F EE AA B6 37 C2 5C 79 20 2F 56 96 01 F4 8F 30 93 D9 0A 7E
14:56:38
RX: 7E A0 37 61 03 52 0E 3A E6 E7 00 CF 29 30 00 00 00 46 C9 79 51 75 97 3D 12 85 31 42 89 9D 33 F8 7B ED 3A A9 F7 BB 50 CE CE AA 0F 43 85 F5 23 16 B8 CD B8 DE EA 75 5D F0 7E
14:56:48 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A8 89 03 61 54 D6 2C E6 E6 00 C9 82 01 5C 30 00 00 00 4B E6 8C CA 1D BF 7F 33 3A 47 61 98 59 4B 6E 1E FB 0C E8 48 E1 34 7D 61 B9 F4 54 F3 3B 90 47 C8 D2 49 FC BB 33 34 E0 BF 5C FC D6 45 85 5A 89 8C 18 40 B3 E6 E8 7F 0B 80 51 F3 02 C6 1E 67 33 F2 F6 70 03 CF C3 BB BC 88 AE DA 87 2F 37 49 4F 8C 54 E7 17 E0 5B DD C9 CC 6F 45 4B B8 F7 82 3E F4 8E 6C 6C 2A 36 2B B5 83 43 3A B4 53 C1 79 CA 2B A9 18 B7 E2 D4 ED AB 7E
14:56:48
TX: 7E A8 89 03 61 56 C4 0F 78 7D DB 15 2E E3 F4 EF 1F A2 E7 8C 14 1A 43 59 D9 E1 5D 3E FF 4E 0C 17 92 E8 99 8A 20 0A E4 7E F0 7B 45 9B 41 37 06 D4 A6 13 3E F0 03 E3 C9 B5 9F 90 39 33 4C 82 98 9F 01 9E 87 8F D2 EE 42 ED C6 1C 9D BD BD 6E B8 8F 98 17 17 D1 26 66 1B DE 1E 71 F8 16 F9 7A 6A B8 EE 7A 91 A6 21 E1 08 D0 DA F3 AC A5 44 93 77 BE 76 CD 38 EF 5B D3 57 0D 1D 25 D4 B0 62 9A F4 9A 55 F1 07 16 07 8C 3F 25 B4 E0 7E
14:56:49
14:56:49 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A0 6C 03 61 58 47 66 C6 F5 52 8C 28 65 C3 FB EB 70 C1 DF 94 49 BD 86 22 0E C4 17 34 E2 BE E8 A9 1A 48 69 49 77 EC 22 47 4D 69 DF 12 49 4F 7A 0F 18 67 3F B4 1E 99 93 22 71 38 41 F0 67 FF 80 69 FB 00 BE 19 A4 A3 3C C1 38 E0 F6 6A B7 B4 65 1C 29 CE 77 29 6D 0B CE D2 9B 7F 3C B0 6C 3B BD FB D2 A8 65 BB 23 87 64 2A D3 56 DC 1C 7E
14:56:50
RX: 7E A0 23 61 03 B4 7B 09 E6 E7 00 CD 15 30 00 00 00 47 48 FE F8 DA CD E3 CC F9 7B 6F 7C 9E 9F 78 57 C2 88 DD 7E
14:56:50 Reading object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A0 2C 03 61 7A E0 72 E6 E6 00 C8 1E 30 00 00 00 4C B1 DE C2 34 A4 64 E9 08 F6 9E 12 8D FC 98 77 74 44 07 69 67 98 2D 70 82 34 A2 55 7E
14:56:50
RX: 7E A8 89 61 03 D6 DC 6D E6 E7 00 CC 81 BC 30 00 00 00 48 7B 29 61 AE B0 D4 9E 91 DF 22 A7 34 1E 9D 5D 7B 66 C8 92 EB E2 B9 0E 09 CA 1A 45 1F 2D 3B 48 D6 8B C3 9C 33 03 18 2D C7 FA 70 BB AD 11 5D 59 BD DB 30 E7 9D 3E 97 E2 CF 9F 90 45 17 65 BC 28 B9 BB AA 64 07 18 E2 60 64 03 E4 C5 A3 47 22 FA FD 5C 8A 8B 2C 20 14 30 7A C7 A1 38 CB 42 4B 3F F8 94 A9 6B 98 E1 92 DF 08 D1 70 F0 A3 7A 24 9B 6B E2 68 97 AF 45 57 10 7E
14:56:50
TX: 7E A0 07 03 61 91 7B 64 7E
14:56:50
RX: 7E A0 4B 61 03 D8 2D DC FE 10 44 69 89 8B B8 8B 7F AE 4B BB BC 91 CF 63 62 C1 1A 50 89 98 07 31 B3 CA 1A 9D D7 59 A3 A9 16 2D DE 81 46 DD 9E 16 19 18 A6 A5 A2 8E 1B C2 DA 55 45 D0 D9 DE 9C 68 FF 88 E4 D2 4F 09 05 4E 00 94 21 40 7E
14:56:50
TX: 7E A0 26 03 61 BC 74 0D E6 E6 00 C8 18 30 00 00 00 4D 2E 83 2C 0E 58 F3 A5 41 E4 AD 24 F3 59 19 C1 4A 50 C9 56 3E 24 7E
14:56:50
RX: 7E A8 89 61 03 FA B2 86 E6 E7 00 CC 81 BA 30 00 00 00 49 FA 28 CD 5C 56 14 46 66 79 E4 E1 4D DF 92 2A 27 CD F8 58 75 CB A7 19 1B A2 B6 93 E6 C2 92 79 39 EA F7 F5 CE BD ED 8B CF 8C CA E4 C2 35 6E 7A EF 46 79 18 55 B1 57 6A 8C 00 AB C3 12 2D D0 E3 5E FA 01 05 07 D4 44 0D 9E 3A 60 11 FA 93 8E 1D E9 8C 75 05 A2 7B AD 91 EB F1 14 1E 84 C7 F1 3A F3 EF 31 04 BB 71 9B 0C DD A1 67 1B FE D1 0E 98 99 2C E9 82 6E 54 CF F3 7E
14:56:50
TX: 7E A0 07 03 61 D1 7F 26 7E
14:56:51
RX: 7E A0 49 61 03 FC 7D 82 E3 B1 55 0B 10 B0 E8 39 5C F4 DA CB 9E 1C 6B 53 41 BD 11 33 50 C4 1E 28 1E 41 ED E2 AE B5 5E 44 18 6D 05 2B C3 51 9F 64 4A B7 90 EC 1E 9C 99 ED EA D1 1E 50 F4 6C 45 2E DC 7D 0B E5 55 F1 12 F2 CE BB 7E
5 months 1 week ago
Hi, Your data is encrypted…
Your data is encrypted. I also need the block cipher key.
intellismartinfra
5 months 1 week ago
Thanks, Mikko, for quick…
Thanks, Mikko, for quick response!!
Please find the below the keys as well as new log aligned with this shared key:
Block Cipher Key: bbbbbbbbbbbbbbbb
HLS: wwwwwwwwwwwwwwww
=============Getting "Service Not Allowed" Error after Few packets transfer==========
19:06:09 Send SNRM request.
19:06:09
19:06:09 Send AARQ request.
19:06:09
19:06:09
RX: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 00 10 FC 08 7E
19:06:09 Disconnect request
19:06:09
19:06:09
TX: 7E A0 6B 03 61 10 2A FF E6 E6 00 60 5D A1 09 06 07 60 85 74 05 08 01 03 A6 0A 04 08 49 4E 54 31 32 33 34 35 8A 02 07 80 8B 07 60 85 74 05 08 02 02 AC 12 80 10 58 3E 02 3B 31 11 0F 59 74 31 4D 5F 63 50 18 65 BE 23 04 21 21 1F 30 00 00 00 11 43 C1 D7 C7 00 7D 75 30 80 69 CE 21 9E A6 8D 17 28 27 5C C2 8E 74 53 E0 08 40 DC A8 7E
19:06:10
RX: 7E A0 77 61 03 30 AD 6C E6 E7 00 61 69 A1 09 06 07 60 85 74 05 08 01 03 A2 03 02 01 00 A3 05 A1 03 02 01 0E A4 0A 04 08 49 4E 54 31 32 33 34 35 88 02 07 80 89 07 60 85 74 05 08 02 02 AA 12 80 10 61 62 63 64 65 66 67 68 69 6A 6B 6C 6D 6E 6F 70 BE 23 04 21 28 1F 30 00 00 00 10 3E AE 90 C8 E9 C6 11 46 5E CF 9C 35 63 D3 75 84 EB EC 4A EE 23 AF 80 E1 A2 BC C5 12 7E
19:06:10 Authenticating.
TX: 7E A0 3E 03 61 32 7B 46 E6 E6 00 CB 30 30 00 00 00 12 E7 A8 B7 78 C0 76 D5 17 94 87 0C E9 14 27 0C 22 19 4B BB C7 F1 D2 85 E2 DD D1 EC 1E 1E B4 FA E3 5A 34 37 0B 13 7D 50 42 04 56 B6 ED B8 7E
19:06:10
RX: 7E A0 37 61 03 52 0E 3A E6 E7 00 CF 29 30 00 00 00 11 85 C0 16 C7 07 22 63 24 9D 59 07 58 5D 62 99 78 4D 52 0A AF B0 91 F2 68 B1 16 5C 10 F8 11 35 95 FA 13 5E 3C 9B 5C 7E
19:06:26 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A8 89 03 61 54 D6 2C E6 E6 00 E0 01 00 01 00 00 82 01 F9 C9 82 02 00 30 00 00 00 13 C4 0D 9E 4C A4 79 D2 0A D1 EF 1A B9 72 F6 6D D1 31 8C BB 28 1C 22 0B 57 D7 23 D8 95 54 7C FF 9E 3F F9 16 9A CE B9 67 80 8B F8 79 F8 2B 1F DE 0C C0 AF 1D AD 97 3F B5 E9 AD EA F1 46 4A CC F6 9B C2 7E FA F2 2B 95 2A A0 31 04 F5 D3 2D 1D 60 39 70 B3 6C 4C 50 76 B7 99 55 E4 F0 B2 96 31 C4 35 55 C7 8D 09 11 9E FA 71 5A BD 1E 78 09 7E
19:06:26
TX: 7E A8 89 03 61 56 C4 0F B4 8B F5 32 DA 02 FD AF C5 66 89 D1 15 9D AD 23 64 E6 F9 46 D8 D4 A3 34 7C 68 5D 00 11 80 A1 5A BB E1 49 03 07 0F 25 D1 15 2D 15 59 E8 06 74 0A 7D 6F 79 64 DD 15 3F C3 AF 7F E2 F7 29 7D FD 98 09 DD 63 F7 54 48 DF 3F 82 24 53 DB BF 2D 16 C6 2C C2 D2 0A 69 82 F2 0B 04 10 19 BD 0A C4 68 F4 74 18 8E 65 B2 3D FA D5 45 87 30 E6 B7 11 71 27 11 CC E8 9B 23 B7 58 62 77 99 F3 22 38 B4 B8 99 3F 46 7E
19:06:26
TX: 7E A8 89 03 61 58 BA E6 CC 45 F9 72 D5 E5 F7 7E 9C 4E AE 57 36 A3 9A BF E6 DE DF 3E 1B E9 27 7D 19 64 D4 94 39 B8 6F BE A6 95 B1 F6 36 6C AA F7 06 68 7C C6 C0 86 84 80 47 2C 53 3B D7 43 D4 40 8B 5B CB A6 65 F8 CE C1 17 7A 2E 93 1D 99 64 BC 5F DA F9 E1 5F 7A 2A 81 E8 52 36 3A D5 D9 CD F7 EB A6 38 EC C1 6E 77 02 21 D1 54 64 77 5C 8A BB 75 1E 7C F9 5E 3C 4C 5B 42 33 81 E2 59 95 79 8C CF 7B C1 B4 6F DC 7A D4 58 F0 7E
19:06:27
19:06:27 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A8 89 03 61 5A A8 C5 D0 30 07 CF 28 C2 0E 51 D1 E6 51 41 E9 93 C1 4E 86 F2 3C FD AF 89 CE 20 96 F7 4E 10 A5 B9 CE 94 33 81 AF A2 02 B9 76 DE EA 6C A3 FA 82 06 F5 B2 1B 30 3D 55 FE 0A 47 32 5B 0A 2A D1 55 25 92 26 FD 1A 7B 41 0C 25 59 EC 31 2E 72 DD 19 9C 28 B8 14 85 76 75 1E 1F 84 35 12 6A 44 BF C2 4D 56 B3 7D CA 8B 78 81 13 A8 EA 66 61 47 A8 46 25 C2 0E 4E D0 F4 C2 8A 38 92 2D 92 77 EB A0 24 E3 A4 83 F7 1E 7E
19:06:27
TX: 7E A0 0E 03 61 5C F1 80 F4 9D 66 E2 CE 49 7D 7E
19:06:27
========Successful Transfer : only after few tariff rate deletion to reduce the data payload=============
19:08:36 Send SNRM request.
19:08:36
19:08:36 Send AARQ request.
19:08:37
19:08:37
RX: 7E A0 15 21 03 52 5D 8A E6 E7 00 C4 01 C1 00 06 00 00 00 12 EE 2B 7E
19:08:37 Disconnect request
19:08:37
19:08:37 Send SNRM request.
19:08:37
19:08:37 Send AARQ request.
TX: 7E A0 6B 03 61 10 2A FF E6 E6 00 60 5D A1 09 06 07 60 85 74 05 08 01 03 A6 0A 04 08 49 4E 54 31 32 33 34 35 8A 02 07 80 8B 07 60 85 74 05 08 02 02 AC 12 80 10 45 29 37 2F 78 1A 4A 29 61 68 4E 43 39 1A 67 2C BE 23 04 21 21 1F 30 00 00 00 13 04 0C 5F 4C B6 26 CD 03 D1 8D FB ED 8D 08 99 18 6C 5B A7 EC 1D 75 85 BE 0E 62 0F EF 7E
19:08:37
RX: 7E A0 77 61 03 30 AD 6C E6 E7 00 61 69 A1 09 06 07 60 85 74 05 08 01 03 A2 03 02 01 00 A3 05 A1 03 02 01 0E A4 0A 04 08 49 4E 54 31 32 33 34 35 88 02 07 80 89 07 60 85 74 05 08 02 02 AA 12 80 10 61 62 63 64 65 66 67 68 69 6A 6B 6C 6D 6E 6F 70 BE 23 04 21 28 1F 30 00 00 00 12 2C A9 70 27 D0 72 D5 1F 8C 9A F1 E8 15 29 EB 9B 76 FA 64 9A 9B 1F 1E DA BE 9E 8F D4 7E
19:08:37 Authenticating.
TX: 7E A0 3E 03 61 32 7B 46 E6 E6 00 CB 30 30 00 00 00 14 AF DB C1 B7 2D 0D 06 E6 8F D0 A1 2A 1B 65 1F 83 18 46 27 00 47 75 BC 7F 6C F9 8B DC F9 42 C5 7A ED D2 DF 18 E8 EE CF 8B D1 05 13 6C 42 7E
19:08:37
RX: 7E A0 37 61 03 52 0E 3A E6 E7 00 CF 29 30 00 00 00 13 C2 0D 9E 4C B1 79 DB 17 D4 CA B6 F2 EA F2 B0 83 0A 54 11 87 A2 09 81 F2 80 EA 28 D5 20 FA 16 10 FB 98 49 89 4A BB 7E
19:08:53 Writing object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A8 89 03 61 54 D6 2C E6 E6 00 C9 82 01 C7 30 00 00 00 15 56 E2 CD 68 5A B1 9E C7 CE 86 25 80 EB BC CE 6F 06 90 1E DC B3 98 04 73 80 A5 FE 7F DD 6E 3E 59 42 AD 87 94 17 C7 5D 66 F7 97 42 6C A1 65 0A 11 AB 52 77 45 29 A5 F5 5A 53 4A 8B 7B 7F EA A2 11 0A 06 82 15 2F 8A 75 8D 08 8B BD 88 7F EC D2 DE 2A 43 71 36 3C 05 A9 DB 3D A7 98 EE 00 D6 EF FE 75 EB CE 02 14 50 20 E3 DE 27 E1 CF E2 34 D4 74 AF B1 E4 B9 0A CC 7E
19:08:53
TX: 7E A8 89 03 61 56 C4 0F D9 8A DA 97 E9 3F 8E 34 0B 13 0E 1D D2 D0 53 A1 98 B8 D4 EA 4D 4C D6 2F D6 DB 22 B0 BA 0D 72 20 5C 92 0F 43 16 1E A0 90 18 65 84 8F F8 63 2C B6 FA FB 78 9C 77 31 17 7A 12 73 9C A8 27 A8 2F 17 0E D0 17 BE 0D 7C F9 7C 88 EC 61 9E F1 25 30 1A E3 42 40 D4 FC AF 90 46 F6 D0 F6 62 BB 63 C4 23 5E 63 48 F2 F8 B4 17 20 42 F6 5E CF 6D E3 C5 5B 37 E5 FE 56 E1 6E 4C 11 98 57 32 37 19 8D 7E 84 5E 96 7E
19:08:53
TX: 7E A8 89 03 61 58 BA E6 8D 9C A2 6E 15 F6 FC 29 16 68 17 0B F3 76 B0 A1 49 CA F5 23 29 68 2D 0C 2D 36 A2 BE 97 84 DC 9A 76 57 91 C3 7F E2 12 E7 2D F8 F0 1A 7D FE 99 9A E6 BD 38 52 8B 0A CA 74 91 08 F4 7E 51 DC 28 EA 87 69 95 D3 ED 53 D7 C2 D7 A7 9E C0 92 B7 CC A8 BB 43 A0 FA AC FB 59 65 B8 88 E8 DD BF 81 B1 B2 40 F3 EE 5A 05 AD 3C 53 E9 24 CE 52 EC B7 D4 7B AE 91 E3 4A 75 C6 32 37 AC 67 7A 1A 21 BC 37 98 91 BB 7E
19:08:53
TX: 7E A0 57 03 61 5A B2 C9 11 51 8C 43 7A A5 C0 28 3D 4D BA 8B 4B 4A 7B B4 C2 B2 CF FB 3C 68 54 27 A3 44 91 AE 24 13 70 B7 30 27 C8 E5 50 1D 64 A2 F9 60 3F 66 74 3A 3A 3D 42 CB D9 A6 60 56 C1 A0 0C 55 98 7D 2D 99 4E 02 ED 54 83 01 32 BE 00 5B C6 07 36 FE 84 54 5F AD 7E
19:08:54
RX: 7E A0 23 61 03 D4 7D 6A E6 E7 00 CD 15 30 00 00 00 14 A9 DB C1 B7 62 6F 18 74 AE E5 BB 9E A2 38 21 B5 B2 C7 7E
19:08:54 Reading object 0.0.13.0.0.255, interface ActivityCalendar
TX: 7E A0 2C 03 61 7C D6 17 E6 E6 00 C8 1E 30 00 00 00 16 6E 8A 72 9D 7D 07 6B 8D 13 A9 0A 18 D4 82 E1 A9 AA A7 47 09 C7 E6 6A F0 A7 16 C2 7E
19:08:54
RX: 7E A8 89 61 03 F6 DE 4C E6 E7 00 CC 81 BC 30 00 00 00 15 53 E1 CD 68 4E B1 9E CB CE 07 7A 88 EF BF C8 7C 05 80 17 DF B8 93 03 7A 84 A5 FE 76 DB 67 38 53 42 C3 78 E2 E8 D4 5F 64 FC 90 48 68 A2 65 03 17 A2 54 7D 45 47 5A 83 A5 43 48 8A 70 78 E5 A6 17 0A 0F 84 1C 29 80 75 E3 F7 FD 42 99 7D EC D9 D9 29 47 7B 36 35 03 A0 DD 37 A7 F6 11 76 29 F9 FC 72 E0 C9 02 10 59 20 EA D8 2E E7 C5 E2 5A 2B 02 50 A6 E6 BF D2 68 33 7E
19:08:54
19:08:54
RX: 7E A0 4B 61 03 F8 2F FD 8D DC 93 E6 3F 87 32 02 15 04 1D BC 2F 25 5E 8C BA D1 E1 4A 57 D2 3D D6 D2 DB B9 BC 07 72 4E A3 E4 F0 56 14 1A AB 97 04 61 91 8F F1 9A 25 B0 F0 FB 16 63 01 CE 0D 0C 8E 85 4D DC 30 D7 5E D1 50 91 26 84 DA 7E
19:08:54
TX: 7E A0 26 03 61 BE 66 2E E6 E6 00 C8 18 30 00 00 00 17 A4 AD 25 99 92 6E 84 E7 9F 0E E7 35 1B 6C EF 2B 43 3B F4 CF 32 7E
19:08:55
RX: 7E A8 89 61 03 1A BC 61 E6 E7 00 CC 81 BA 30 00 00 00 16 6A 89 72 9D 69 07 6B 82 13 28 6B 13 D6 36 82 65 A1 0E 42 FD 9A AF 76 91 F6 37 FA 62 DB 88 29 4F 4D 91 D5 9F 59 9A 45 2D 36 7B 04 07 1C C0 9B 14 63 37 BE 24 6D E1 C2 D7 5D 65 ED BC 79 1C 4F 0C 7B 0C 31 0A 1A CB 47 D4 D8 1F 36 67 25 1F 62 A8 24 07 21 2F D4 24 10 52 1F 0D 1E 27 EE CD 73 C8 11 15 59 9B 6E C0 8F AF 73 9A 25 69 D0 9A 4D E7 B9 7C 2A 46 01 EB 89 7E
19:08:55
19:08:55
RX: 7E A0 49 61 03 1C 73 65 13 10 14 D8 26 F6 18 F3 C4 A5 68 00 A4 AC DA 76 4C 72 A6 1C 09 38 BA C0 39 DF A5 44 77 2D 4E 51 C9 DE 0A CF 27 94 93 67 72 5D 38 99 35 DA D3 38 14 8A DC D0 05 1D 22 DD 0C 21 FD 50 F7 A2 B7 F4 3B 13 7E
19:08:55
TX: 7E A0 26 03 61 F0 1C 85 E6 E6 00 C8 18 30 00 00 00 18 24 8E D8 45 A5 03 EB FD 9E 9A 25 D7 45 7D 38 0B 8A E8 0D 78 0F 7E
19:08:55
RX: 7E A0 68 61 03 3E 8B F4 E6 E7 00 CC 5A 30 00 00 00 17 A0 AD 25 99 92 6E 85 B4 4F 6F 1F 64 42 87 DB B1 1C E7 B4 A1 20 35 9E 9C 62 81 27 6C F6 C3 F4 E2 0E 66 C1 91 0A 84 3F 9D 84 9D C4 10 3D 0F B6 DA F9 63 1D 2D FB 55 BD 1F B6 34 35 F7 E5 B9 7F 77 0E 39 16 EC 10 15 28 5E 48 AB 16 29 98 44 0F 49 3F 47 0F C2 C9 A2 DB 7E
19:08:55
TX: 7E A0 26 03 61 12 00 41 E6 E6 00 C8 18 30 00 00 00 19 10 CE 6B B3 8C 11 81 19 93 13 34 0C 94 6A 75 BA 9B F3 72 03 F9 7E
19:08:55
RX: 7E A0 55 61 03 50 8E B9 E6 E7 00 CC 47 30 00 00 00 18 20 8E D8 44 A5 03 E9 02 F5 02 3F CD D3 8C CB 67 59 50 6F 02 49 02 2B 9E DC E2 55 49 9D 9E 19 27 E1 EF ED 16 9E F6 D5 C4 BE 57 FC 34 A6 7C B1 6F ED 36 9E F8 C2 38 F1 DA 7C 51 D1 7C 52 48 99 F7 1C BF 50 C9 7E
