By Digambar Patil , 14 February, 2017
Forums
General discussion

Dear sir,
we are using indian standard as a manufacturer for event reading.
while taking reading from the tool , response from the tool is accurately come as per DLMS standard.

There is a no problem with data response ....but the actual reading in the table shown in tool is not coming.
Total columns created are totaly blank..
what is the problem?....please suggest me..
Thanks in advance.
The response is as shown below.

Profile picture for user Kurumi

Kurumi

9 years 5 months ago

IS

Dear Sir,

Can you read your columns example GXDLMSDirector and send log to me by email.
You can refresh only one profile generic columns selecting that profile generic and selecting Refresh under File menu.

BR,

Mikko

Profile picture for user Kurumi

Kurumi

9 years 5 months ago

Events

Hi,

Your meter is returning columns that are not standard structure of DLMS.
http://www.gurux.fi/GuruxDLMSTranslator?pdu=6135A109060760857405080101A…

BR,

Mikko

Digambar Patil

9 years 5 months ago

event

Dear sir,
what should i do now?
which type of changes are required?
plz suggest me.
Thanks.

Profile picture for user Kurumi

Kurumi

9 years 5 months ago

Structure

Dear Sir,

Can you ask meter manufacturer to fix this?

BR,

Mikko

Profile picture for user Kurumi

Kurumi

9 years 5 months ago

Profile generic columns.

Dear Sir,

Your meter is returning data like this:
http://www.gurux.fi/GuruxDLMSTranslator?pdu=C401C1000101020412000700090…

Correct data is someting like this.
http://www.gurux.fi/GuruxDLMSTranslator?pdu=C401C1000102020412000809060…

BR,
Mikko

  • Create new account
  • Reset your password

Hire Us!

Latest Releases

  • Mon, 07/27/2026 - 12:37
    gurux.dlms.cpp 9.0.2607.2701
  • Thu, 07/23/2026 - 16:19
    gurux.dlms.java 4.0.96
  • Thu, 07/09/2026 - 14:34
    Gurux.DLMS.Python 1.0.201
  • Fri, 06/26/2026 - 16:32
    Gurux.Service 3.0.2606.2601
  • Wed, 06/24/2026 - 08:36
    Gurux.DLMS.Python 1.0.200

New forum topics

  • Service not known error on gprs communication
  • Help Needed: Interfacing Saral 100 Energy Meter with Microcontroller via RS232
  • Connecting Meter to Agent via serial
  • Reading block profile with Compact array
  • DLMS server - serving multiple similar datasets gathered from multiple meters across distinct logical addresses
More

Who's new

  • CTKNhZElptjSlOrpkXl
  • YCbccqfLGRMnlCWoJhXP
  • Malcolmactig
  • mhliang
  • Kevinmug
RSS feed
Privacy FAQ GXDN Issues Contact
Follow Gurux on Twitter Follow Gurux on Linkedin