Hello.
I use the event log 0.1.99.98.4.255.
I create a device in ami, read the event log, the number of events is 51 (attribute with index 7 in table GxTask). An event occurs in the counter. I read the log data, in attribute 7 the number is 52 (table GxTask), the number of log entries in the table is 51 (table GxValue).
Please tell me what could be the reason.
GuruxDirector reads logs correctly.

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

What is the timestamp of the new event? All profile generics are reading only the data that has occurred after the last succeeded read. Verify first that it's newer.

BR,
Mikko

MNN

5 years 7 months ago

First reading of the event

First reading of the event log:

Send SNRM request.7E A0 07 03 0F 93 2C B8 7E
TX: 10:22:32 7E A0 07 03 0F 93 2C B8 7E
RX: 10:22:32 7E A0 1E 0F 03 73 E3 69 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
Parsing UA reply.81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01
Parsing UA reply succeeded.
Send AARQ request
TX: 10:22:32 7E A0 2B 03 0F 10 D8 16 E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 00 1E 1D FF FF C5 E4 7E
RX: 10:22:32 7E A0 37 0F 03 30 4C 6F E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07 58 26 7E
Parsing AARE reply61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07
Parsing AARE reply succeeded.
Reading: 0.1.99.98.4.255
TX: 10:22:32 7E A0 19 03 0F 32 4C 61 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 00 AD 59 7E
RX: 10:22:32 7E A8 89 0F 03 52 A6 BA E6 E7 00 C4 01 C1 00 01 34 02 02 09 0C 07 DC 01 18 FF 11 11 1C FF 80 00 20 11 28 02 02 09 0C 07 DC 01 1B FF 11 2D 26 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 43 A8 7E
TX: 10:22:32 7E A0 07 03 0F 51 32 5D 7E
RX: 10:22:33 7E A8 89 0F 03 54 90 DF 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 A2 D5 7E
-TX: 10:22:33 7E A0 07 03 0F 71 30 7C 7E
RX: 10:22:33 7E A8 89 0F 03 56 82 FC 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 06 C2 7E
-TX: 10:22:33 7E A0 07 03 0F 91 3E 9B 7E
RX: 10:22:33 7E A8 89 0F 03 58 FC 15 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 13 44 7E
-TX: 10:22:33 7E A0 07 03 0F B1 3C BA 7E
RX: 10:22:33 7E A8 89 0F 03 5A EE 36 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 B9 F5 7E
-TX: 10:22:33 7E A0 07 03 0F D1 3A D9 7E
RX: 10:22:33 7E A8 89 0F 03 5C D8 53 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 A6 10 7E
-TX: 10:22:33 7E A0 07 03 0F F1 38 F8 7E
RX: 10:22:33 7E A8 89 0F 03 5E CA 70 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 2B 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 29 02 02 09 0C 07 E5 02 05 FF 08 2F 03 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 08 34 1D 00 80 00 05 11 2B 02 02 09 0C 07 7C 71 7E
-TX: 10:22:33 7E A0 07 03 0F 11 36 1F 7E
RX: 10:22:34 7E A0 3A 0F 03 50 C5 87 E5 02 05 FF 08 37 16 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 09 35 2E 00 80 00 05 11 2B 02 02 09 0C 07 E5 02 05 FF 09 35 3A 00 80 00 05 11 2C 1C 29 7E
+Reading: 0.1.99.98.4.255
TX: 10:22:34 7E A0 19 03 0F 34 7A 04 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 10:22:35 7E A0 36 0F 03 72 E1 12 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 10:22:35 7E A0 19 03 0F 56 6E 44 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 10:22:35 7E A0 15 0F 03 94 47 3A E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 10:22:35 7E A0 19 03 0F 78 12 8C E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 10:22:35 7E A0 12 0F 03 B6 76 6F E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 10:22:35 7E A0 19 03 0F 9A 0E 48 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 10:22:35 7E A0 22 0F 03 D8 FC A9 E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 10:22:35 7E A0 19 03 0F BC 3A 0C E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 10:22:35 7E A0 15 0F 03 FA 3F B0 E6 E7 00 C4 01 C1 00 06 00 00 00 34 DA 6F 7E
Reading: 0.1.99.98.4.255
TX: 10:22:35 7E A0 19 03 0F DE 2E 4C E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 10:22:35 7E A0 15 0F 03 1C 07 32 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

The number of records is 52.
Events are generated.

Second reading of the event log:

Send SNRM request.7E A0 07 03 0F 93 2C B8 7E
TX: 10:25:37 7E A0 07 03 0F 93 2C B8 7E
RX: 10:25:37 7E A0 1E 0F 03 73 E3 69 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
Parsing UA reply.81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01
Parsing UA reply succeeded.
Send AARQ request
TX: 10:25:37 7E A0 2B 03 0F 10 D8 16 E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 00 1E 1D FF FF C5 E4 7E
RX: 10:25:37 7E A0 37 0F 03 30 4C 6F E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07 58 26 7E
Parsing AARE reply61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07
Parsing AARE reply succeeded.
Reading: 0.1.99.98.4.255
TX: 10:25:37 7E A0 4C 03 0F 32 0D DA E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 01 01 02 04 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 09 0C 07 E5 02 05 FF 09 35 3A FF FF 4C 00 09 0C 07 E5 02 05 FF 0B 00 00 FF FF 4C 00 01 00 21 56 7E
RX: 10:25:37 7E A0 5A 0F 03 52 33 3D E6 E7 00 C4 01 C1 00 01 04 02 02 09 0C 07 E5 02 05 FF 09 35 2E 00 80 00 05 11 2B 02 02 09 0C 07 E5 02 05 FF 09 35 3A 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 0A 17 21 00 80 00 05 11 2B 02 02 09 0C 07 E5 02 05 FF 0A 17 23 00 80 00 05 11 2C 8C E8 7E
Reading: 0.1.99.98.4.255
TX: 10:25:37 7E A0 19 03 0F 54 7C 67 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 10:25:37 7E A0 36 0F 03 74 D7 77 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 10:25:37 7E A0 19 03 0F 76 6C 65 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 10:25:37 7E A0 15 0F 03 96 55 19 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 10:25:38 7E A0 19 03 0F 98 1C 6B E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 10:25:38 7E A0 12 0F 03 B8 08 86 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 10:25:38 7E A0 19 03 0F BA 0C 69 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 10:25:38 7E A0 22 0F 03 DA EE 8A E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 10:25:38 7E A0 19 03 0F DC 3C 6F E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 10:25:38 7E A0 15 0F 03 FC 09 D5 E6 E7 00 C4 01 C1 00 06 00 00 00 36 C8 4C 7E
Reading: 0.1.99.98.4.255
TX: 10:25:38 7E A0 19 03 0F FE 2C 6D E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 10:25:38 7E A0 15 0F 03 1E 15 11 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

Last 2 entries in Director after first reading:
05.02.2021 9:53 43
05.02.2021 9:53 44

Last 4 entries in Director after second reading:
05.02.2021 9:53 43
05.02.2021 9:53 44
05.02.2021 10:23 43
05.02.2021 10:23 44

MNN

5 years 7 months ago

Hello.

Hello.
When re-reading, requests to read attribute 2 do not go away, as you can see from the message above, the events have a timestamp later than the events that were read the first time.
Can you tell me what could be the reason?

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

I checked this GXDLMSDirector log, but it doesn't tell why the amount of the rows is different in AMI. Can you add a log from AMI so I can check it?

When you read the events the first time it will read all data from the meter. When you read the meter a second time you try to read with a given range. You give start time and end time.
5.2.2021 9.53.58+03:00
5.2.2021 11.00.00+03:00

Meter returns 4 rows.

MNN

5 years 7 months ago

Hello.

Hello.
As far as I know, in AMI you cannot set the period for requesting profiles from the device. Option "All" is set in AMI. Where can this period come from and why, in this case, new data are not written to table GXValue, although in table GXTask the correct quantity is returned (attribute 7) and the last event is written in attribute 2.
GuruxDirector reads events correctly, the problem occurs in GuruxAMI. The message above contains a log of GuruxAMI.

Image

MNN

5 years 7 months ago

There are 73 records left in

There are 73 records left in the table GXValues after re-read.

Image
Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

All data is read for the first time. The reason for this is that all the meters are not supporting read by entry. and we simply don't know what is the first row.

After that new rows are read after the last read row.

Are only those two rows missing all the time and the amount of the missing rows are not increasing?
If I read correctly from your DB there should be 75 rows and now there are 73. Is that correct?

BR,
Mikko

MNN

5 years 7 months ago

Hello.

Hello.

Yes, that's right, there are 75 records in the device, in base 73. On an empty base, all events are read for the first time, on subsequent readings of the object, events are not accumulated in the database, clearing table GXValues does not help.

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

Can you add hex trace from Gurux.DLMS.AMI so I can verify the bytes?

BR,
Mikko

MNN

5 years 7 months ago

Hello.

Hello.

Empty base created, first read of device log (75 events):

Send SNRM request.7E A0 07 03 0F 93 2C B8 7E
TX: 09:47:50 7E A0 07 03 0F 93 2C B8 7E
RX: 09:47:50 7E A0 1E 0F 03 73 E3 69 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
Parsing UA reply.81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01
Parsing UA reply succeeded.
Send AARQ request
TX: 09:47:50 7E A0 2B 03 0F 10 D8 16 E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 00 1E 1D FF FF C5 E4 7E
RX: 09:47:50 7E A0 37 0F 03 30 4C 6F E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07 58 26 7E
Parsing AARE reply61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07
Parsing AARE reply succeeded.
Reading: 0.1.99.98.4.255
TX: 09:47:50 7E A0 19 03 0F 32 4C 61 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 00 AD 59 7E
RX: 09:47:50 7E A8 89 0F 03 52 A6 BA E6 E7 00 C4 02 C1 00 00 00 00 01 00 82 03 CE 01 4B 02 02 09 0C 07 DC 01 18 FF 11 11 1C FF 80 00 20 11 28 02 02 09 0C 07 DC 01 1B FF 11 2D 26 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 09 00 80 00 20 11 28 02 02 09 63 3B 7E
TX: 09:47:50 7E A0 07 03 0F 51 32 5D 7E
RX: 09:47:51 7E A8 89 0F 03 54 90 DF 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DD 46 7E
-TX: 09:47:51 7E A0 07 03 0F 71 30 7C 7E
RX: 09:47:51 7E A8 89 0F 03 56 82 FC DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 C6 3C 7E
-TX: 09:47:51 7E A0 07 03 0F 91 3E 9B 7E
RX: 09:47:51 7E A8 89 0F 03 58 FC 15 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 4F 42 7E
-TX: 09:47:51 7E A0 07 03 0F B1 3C BA 7E
RX: 09:47:51 7E A8 89 0F 03 5A EE 36 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 5D 57 7E
-TX: 09:47:51 7E A0 07 03 0F D1 3A D9 7E
RX: 09:47:51 7E A8 89 0F 03 5C D8 53 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 A2 D5 7E
-TX: 09:47:51 7E A0 07 03 0F F1 38 F8 7E
RX: 09:47:52 7E A8 89 0F 03 5E CA 70 80 00 20 11 28 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 2B 02 02 09 0C 07 DC 01 01 FF 00 00 03 00 80 00 20 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 2B 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 29 02 02 09 0C 07 E5 02 05 FF 08 2F 03 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 08 34 1D 00 80 00 20 AD 7E
-TX: 09:47:52 7E A0 07 03 0F 11 36 1F 7E
RX: 09:47:52 7E A0 66 0F 03 50 E7 C5 05 11 2B 02 02 09 0C 07 E5 02 05 FF 08 37 16 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 09 35 2E 00 80 00 05 11 2B 02 02 09 0C 07 E5 02 05 FF 09 35 3A 00 80 00 05 11 2C 02 02 09 0C 07 E5 02 05 FF 0A 17 21 00 80 00 05 11 2B 02 02 09 0C 07 E5 02 05 FF 0A 17 23 00 80 00 05 11 2C 28 31 7E
+TX: 09:47:52 7E A0 13 03 0F 34 D4 D8 E6 E6 00 C0 02 C1 00 00 00 01 51 BE 7E
RX: 09:47:52 7E A8 89 0F 03 72 A4 9B E6 E7 00 C4 02 C1 01 00 00 00 02 00 82 01 7A 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 A4 5E 7E
-TX: 09:47:52 7E A0 07 03 0F 51 32 5D 7E
RX: 09:47:52 7E A8 89 0F 03 74 92 FE 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 02 02 09 0C 07 E5 02 0D C3 7E
-TX: 09:47:52 7E A0 07 03 0F 71 30 7C 7E
RX: 09:47:52 7E A8 89 0F 03 76 80 DD 0C FF 0A 2D 0D 00 80 00 0C 11 2B 02 02 09 0C 07 E5 02 0C FF 0A 2D 0E 00 80 00 0C 11 2C 02 02 09 0C 07 E5 02 0C FF 0A 30 09 00 80 00 0C 11 2B 02 02 09 0C 07 E5 02 0C FF 0A 30 0B 00 80 00 0C 11 2C 02 02 09 0C 07 E5 02 0C FF 0B 02 30 00 80 00 0C 11 2B 02 02 09 0C 07 E5 02 0C FF 0B 02 35 00 80 00 0C 11 2C 02 02 09 0C 07 E5 02 0C FF 11 06 32 00 80 00 0C 11 2B 02 02 09 0C 07 E5 02 0C FF 09 7F 7E
-TX: 09:47:52 7E A0 07 03 0F 91 3E 9B 7E
RX: 09:47:52 7E A0 12 0F 03 78 04 40 11 06 36 00 80 00 0C 11 2C 5A 66 7E
+Reading: 0.1.99.98.4.255
TX: 09:47:53 7E A0 19 03 0F B6 60 A3 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 09:47:54 7E A0 36 0F 03 9A A7 79 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 09:47:54 7E A0 19 03 0F D8 18 29 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 09:47:54 7E A0 15 0F 03 BC 0D 97 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 09:47:54 7E A0 19 03 0F FA 08 2B E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 09:47:54 7E A0 12 0F 03 DE 38 80 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 09:47:54 7E A0 19 03 0F 1C 30 A9 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 09:47:54 7E A0 22 0F 03 F0 B6 04 E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 09:47:54 7E A0 19 03 0F 3E 20 AB E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 09:47:54 7E A0 15 0F 03 12 79 DB E6 E7 00 C4 01 C1 00 06 00 00 00 4B AA E4 7E
Reading: 0.1.99.98.4.255
TX: 09:47:54 7E A0 19 03 0F 50 58 21 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 09:47:54 7E A0 15 0F 03 34 4D 9F E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

Re-reading the log after events have occurred (77 events):

Send SNRM request.7E A0 07 03 0F 93 2C B8 7E
TX: 09:50:29 7E A0 07 03 0F 93 2C B8 7E
RX: 09:50:29 7E A0 1E 0F 03 73 E3 69 81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01 53 3B 7E
Parsing UA reply.81 80 12 05 01 80 06 01 80 07 04 00 00 00 01 08 04 00 00 00 01
Parsing UA reply succeeded.
Send AARQ request
TX: 09:50:29 7E A0 2B 03 0F 10 D8 16 E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 00 1E 1D FF FF C5 E4 7E
RX: 09:50:29 7E A0 37 0F 03 30 4C 6F E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07 58 26 7E
Parsing AARE reply61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 18 1D 03 E8 00 07
Parsing AARE reply succeeded.
Reading: 0.1.99.98.4.255
TX: 09:50:29 7E A0 4C 03 0F 32 0D DA E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 01 01 02 04 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 09 0C 07 E5 02 0C FF 11 06 36 FF FF 4C 00 09 0C 07 E5 02 10 FF 0A 00 00 FF FF 4C 00 01 00 42 2E 7E
RX: 09:50:29 7E A0 48 0F 03 52 E4 C7 E6 E7 00 C4 01 C1 00 01 03 02 02 09 0C 07 E5 02 0C FF 11 06 36 00 80 00 0C 11 2C 02 02 09 0C 07 E5 02 10 FF 09 30 2F 00 80 00 10 11 2B 02 02 09 0C 07 E5 02 10 FF 09 30 31 00 80 00 10 11 2C F2 5F 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F 54 7C 67 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 09:50:30 7E A0 36 0F 03 74 D7 77 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F 76 6C 65 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 09:50:30 7E A0 15 0F 03 96 55 19 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F 98 1C 6B E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 09:50:30 7E A0 12 0F 03 B8 08 86 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F BA 0C 69 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 09:50:30 7E A0 22 0F 03 DA EE 8A E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F DC 3C 6F E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 09:50:30 7E A0 15 0F 03 FC 09 D5 E6 E7 00 C4 01 C1 00 06 00 00 00 4D 9C 81 7E
Reading: 0.1.99.98.4.255
TX: 09:50:30 7E A0 19 03 0F FE 2C 6D E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 09:50:30 7E A0 15 0F 03 1E 15 11 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

MNN

5 years 7 months ago

It is noticed that after

It is noticed that after reading the event log in table GXAttribute, the date of reading the attribute in field "Read" is set. After that, when reading the event log, no new events are written. If the value of this field is set to "0001-01-01 00:00:00", new events are written to the database.

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

Your meter is returning a strange date-time field. It says that deviation is not used and it's OK, but then there is a skipped flag and it's saying that some of the data is not used.
07E50205FF09352E00800005 //Year and day is skipped.
07E5020CFF0A30090080000C //Hour and Month is skipped.

This will cause that data is not saved to the DB.

You need to ask from the meter manufacturer what is the idea of this? I believe that this a meter issue.

BR,
Mikko

BR,
Mikko

MNN

5 years 7 months ago

Which date and time format

Which date and time format will be correct?

Profile picture for user Kurumi

Kurumi

5 years 7 months ago

Hi,

Hi,

The date format is correct. Problems is Clock_status. Now it's value is 0x20, but in DLSM standard bit #5 is reserved. When data is read next time status is 05. This means that date-time value is invalid and a different clock base is used. This is also an error. I realized that clock status information is not shown to the user.

Because I don't have your meter I can's say for sure what is causing this. Can you select "Ignore Time Zone" from the meter settings in "Advanced" tab? Try to read the meter with GXDLMSDirector and paste trace here. Let see if it will solve the problem.

BR,
Mikko

07DC0101FF00000300800020

MNN

5 years 6 months ago

Hello.

Hello.
Thank you.

The meter manufacturer fixed the date format, but the problem persists. Please see what the problem is now.

An empty sqlite database has been created. First reading of the event log (2 entries).

Reading: 0.1.99.98.4.255
TX: 10:51:07 7E A0 19 03 0F 32 4C 61 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 00 AD 59 7E
RX: 10:51:07 7E A0 36 0F 03 52 E3 33 E6 E7 00 C4 01 C1 00 01 02 02 02 09 0C 07 E5 02 19 FF 0A 1D 20 00 80 00 FF 11 28 02 02 09 0C 00 00 00 00 00 00 00 00 00 00 00 00 11 28 2F 8F 7E
Reading: 0.1.99.98.4.255
TX: 10:51:07 7E A0 19 03 0F 54 7C 67 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 10:51:07 7E A0 36 0F 03 74 D7 77 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 10:51:07 7E A0 19 03 0F 76 6C 65 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 10:51:07 7E A0 15 0F 03 96 55 19 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 10:51:07 7E A0 19 03 0F 98 1C 6B E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 10:51:07 7E A0 12 0F 03 B8 08 86 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 10:51:07 7E A0 19 03 0F BA 0C 69 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 10:51:08 7E A0 22 0F 03 DA EE 8A E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 10:51:08 7E A0 19 03 0F DC 3C 6F E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 10:51:08 7E A0 15 0F 03 FC 09 D5 E6 E7 00 C4 01 C1 00 06 00 00 00 02 6F 3B 7E
Reading: 0.1.99.98.4.255
TX: 10:51:08 7E A0 19 03 0F FE 2C 6D E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 10:51:08 7E A0 15 0F 03 1E 15 11 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

Events generated.
Second reading of the event log (7 entries), but there are still 2 entries in the database.

Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 4C 03 0F 32 0D DA E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 01 01 02 04 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 09 0C 07 E5 01 01 FF 00 00 00 FF FF 4C 00 09 0C 07 E5 02 19 FF 0B 00 00 FF FF 4C 00 01 00 7B 59 7E
RX: 10:52:47 7E A0 12 0F 03 52 5C CE E6 E7 00 C4 01 C1 00 01 00 8A D8 7E
Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 19 03 0F 54 7C 67 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 03 00 75 40 7E
RX: 10:52:47 7E A0 36 0F 03 74 D7 77 E6 E7 00 C4 01 C1 00 01 02 02 04 12 00 08 09 06 00 00 01 00 00 FF 0F 02 12 00 00 02 04 12 00 01 09 06 00 05 60 0B 01 FF 0F 02 12 00 00 1B 43 7E
Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 19 03 0F 76 6C 65 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
RX: 10:52:47 7E A0 15 0F 03 96 55 19 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 19 03 0F 98 1C 6B E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
RX: 10:52:47 7E A0 12 0F 03 B8 08 86 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 19 03 0F BA 0C 69 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
RX: 10:52:47 7E A0 22 0F 03 DA EE 8A E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
Reading: 0.1.99.98.4.255
TX: 10:52:47 7E A0 19 03 0F DC 3C 6F E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
RX: 10:52:47 7E A0 15 0F 03 FC 09 D5 E6 E7 00 C4 01 C1 00 06 00 00 00 07 C2 6C 7E
Reading: 0.1.99.98.4.255
TX: 10:52:48 7E A0 19 03 0F FE 2C 6D E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
RX: 10:52:48 7E A0 15 0F 03 1E 15 11 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

MNN

5 years 6 months ago

I select "Ignore Time Zone"

Hello.
I select "Ignore Time Zone" in GXDLMSDirector and and read the object:

16:53:26 Read object type ProfileGeneric index: 4
TX: 7E A0 1A 02 21 0F 32 6D 7E E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 04 00 7D 0D 7E
16:53:26
RX: 7E A0 16 0F 02 21 52 A8 B4 E6 E7 00 C4 01 C1 00 06 00 00 00 00 7D 18 7E
16:53:26 Read object type ProfileGeneric index: 5
TX: 7E A0 1A 02 21 0F 54 5D 78 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 05 00 A5 14 7E
16:53:26
RX: 7E A0 13 0F 02 21 74 C8 D6 E6 E7 00 C4 01 C1 00 16 01 9A 11 7E
16:53:26 Read object type ProfileGeneric index: 6
TX: 7E A0 1A 02 21 0F 76 4D 7A E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 06 00 CD 3E 7E
16:53:26
RX: 7E A0 23 0F 02 21 96 05 C6 E6 E7 00 C4 01 C1 00 02 04 12 00 00 09 06 00 00 00 00 00 00 0F 00 12 00 00 7C 19 7E
16:53:26 Reading profile generic data 0.1.99.98.4.255
TX: 7E A0 1A 02 21 0F 98 3D 74 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 02 00 AD 59 7E
16:53:26
RX: 7E A0 25 0F 02 21 B8 E1 35 E6 E7 00 C4 01 C1 00 01 01 02 02 09 0C 07 E5 03 01 01 09 32 11 FF FF 4C 00 11 3F D7 1E 7E
16:53:26 Read object type ProfileGeneric index: 7
TX: 7E A0 1A 02 21 0F BA 2D 76 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 07 00 15 27 7E
16:53:26
RX: 7E A0 16 0F 02 21 DA E8 BC E6 E7 00 C4 01 C1 00 06 00 00 00 01 F4 09 7E
16:53:26 Read object type ProfileGeneric index: 8
TX: 7E A0 1A 02 21 0F DC 1D 70 E6 E6 00 C0 01 C1 00 07 00 01 63 62 04 FF 08 00 DD A4 7E
16:53:27
RX: 7E A0 16 0F 02 21 FC DC F8 E6 E7 00 C4 01 C1 00 06 00 00 00 64 5F 3D 7E

Profile picture for user Kurumi

Kurumi

5 years 6 months ago

Hi,

Hi,

When you read data with GXDLMSDirector there is only one row in the meter. When you read the meter with AMI, the meter returns invalid date-time.
<!-- *.*.* 0.00.00 -->
<OctetString Value="000000000000000000000000" />

You need to ask if there is an issue with the meter.

BR,
Mikko

MNN

5 years 6 months ago

Correct me if I'm wrong, in

Correct me if I'm wrong, in file Reader.cs, in loop "foreach (GXStructure row in (GXArray)val)", you must clear flag "read = false", otherwise new records will not be added to the database.

  • Create new account
  • Reset your password

Hire Us!

Latest Releases

  • Wed, 08/26/2026 - 09:04
    Gurux.DLMS.Python 1.0.203
  • Mon, 08/17/2026 - 11:28
    Gurux.DLMS.Python 1.0.202
  • Mon, 08/17/2026 - 09:47
    gurux.dlms.cpp 9.0.2608.1701
  • Mon, 08/17/2026 - 09:25
    gurux.dlms.c 9.0.2608.1701
  • Mon, 07/27/2026 - 12:37
    gurux.dlms.cpp 9.0.2607.2701

New forum topics

  • Security vulnerability report — request for a private contact (GuruxDLMS.c / ANSI C)
  • Topic: Insufficient Memory Error When Reading Class 7 Profile Generic Objects
  • SN ReadResponse returns all-null values when response spans multiple HDLC frames
  • Gurux.Serial.Android 3.0.6 – CH340 (HL-340) USB-Serial Adapter Not Working,
  • Trying to talk to a L&G E360 meter (Using Python Gurux)
More

Who's new

  • Anaglyfos Trading CC
  • cyby
  • Metin Onan
  • ssv007
  • 3nzol3dur
RSS feed
Privacy FAQ GXDN Issues Contact
Follow Gurux on Twitter Follow Gurux on Linkedin