Hi there,
I'm wondering if it is a way to parse the OBIS code which comes into a DLMS answer in order to be able to check that the answer corresponds to the requested OBIS.
It´s because i´m working with PLC meters and a concentrator which sometimes sends the answer to a request twice
thanks in advance!
Hi,
Hi,
The requested OBIS code is not in the meter reply. You need to check if the received reply is a valid answer from the received frame.
BR,
Mikko