I'm having problems to read the profile generic data of a pair of Sagemcom cx1000-6 es meters.
It's energy generation data, not consumption, as the meters are in a photovoltaic installation.
When trying to read from the OBIS 1.0.99.1.0.255 I get an "SCOPE OF ACCESS VIOLATED" error.
Doing a scan also fails after some time and cannot read all the objects.
These meters have been reprogramed by the distributor company to accomodate new legislation about tarification periods.
¿Has anybody faced a similar problem? ¿Is there a "standar" way to read the hourly curve data in tarification periods?
Can you read 1.0.99.1.0.255 if you select "Read all"? All the meters don't support read by entry or range and you need to read all data from the profile generic buffer.
If I select "Read all" the program reads values, but after a while an error appears: "Invalid data type"
I have to say that we were reading these meters correctly but after the distributor reprograming we are not able to read almost anything (we can read the time for example
Hi,
Hi,
Can you read 1.0.99.1.0.255 if you select "Read all"? All the meters don't support read by entry or range and you need to read all data from the profile generic buffer.
BR,
Mikko
Thanks for your response!
Thanks for your response!
If I select "Read all" the program reads values, but after a while an error appears: "Invalid data type"
I have to say that we were reading these meters correctly but after the distributor reprograming we are not able to read almost anything (we can read the time for example
Hi,
Hi,
This looks like a meter issue. You need to ask if there is a firmware update for the meter.
BR,
Mikko