I have a EMH LZQJ-XC in combination with the EMH Variomod-XC LTE. I can connect to the meter with their software (Combimaster), but not with Gurux DLMS Director. All setting are OK. Beneath the log if I connect:
07:49:19 07:49:19.756 Info Opening
07:49:19 07:49:19.756 Info Client Settings: Protocol Tcp Host: 188.207.43.244 Port: 8000
07:49:20 07:49:20.346 Info Open
07:49:20 Send SNRM request.
TX: 7E A0 0A 00 02 7E 73 41 93 A9 63 7E
07:49:20 07:49:20.856 Sent 7E A0 0A 00 02 7E 73 41 93 A9 63 7E
07:49:30 Failed to receive reply from the device in given time.
07:49:30 Send Disconnect request.
TX: 7E A0 0A 00 02 7E 73 41 53 A5 A5 7E
07:49:30 07:49:30.870 Sent 7E A0 0A 00 02 7E 73 41 53 A5 A5 7E
07:49:40 Failed to receive reply from the device in given time.
07:49:40 07:49:40.878 Info Closing
07:49:40 07:49:40.878 Info Closed
So you are not using direct TCP/IP connection to the meter. You have Moxa, etc in the middle.
I'm glad that this is solved. Serial port settings might sometimes cause a lot of pain.
Change the Logical server from 10 to 0. Is 10077865 serial number of the meter?
EMH came with the following
EMH came with the following solution: Unselect Create 7E1 parity. I can now connect to the meter and all parameters. Thank you.
Solved.